So after some interesting discussions here, I set about trying to rectify my electrical supply issues.
I did some further research on 208 3P and 110 1P in the same box.
Had a look at the neighboring shops - that had been professionally upgraded.
Had a chance to speak to a local electrician.
Reached out to a few online forums.
What I learned was, 1p and 3P in the same box is fully acceptable under the California version of the NEC, and very common.
The caveat being, your "load center" - aka breaker box - needs to be listed to have both in it.
Here is a diagram of how it is to be wired:
With this knowledge in hand, I decided that my best option was to replace the existing box with a new, larger, higher amp one.
I opted for a 18 place, 36 circuit, version - largely because it was available at the local supply shop and very reasonable in cost ($300).
This is the first time I have ever replaced a box, much less a 3P one, so I watched some YouTube and followed good practice.
- The box is proceeded by a shut off.
- I used anti corrosion grease on all my large incoming power/neutral/ground lines.
- Code calls for red/blk/blu - which I maintained. On existing areas I needed to utilize, I used colored tape to mark the lines as per code.
- On my 208V 1P, where the electrician ran some of the grounds to ground, and some to neutral - I rewired to be all to ground.
Editors note: turns out that in a 208 1P, if you run ground to neutral, you risk electrifying the "ground" wire if you have a fault where a hot touches the metal casing of your machine. = bad.
After testing to ensure nothing was live - I tackled the birds nest of an old box that existed.
All out of space/ grounds going to neutral/...
Tidied up a bit, room for 3 @ 3 phase breakers to allow individualized circuits for each of the big machines.
A bit of capacity should I need to expand - though not much.
White 6AWG marked with blue tape at both ends to signify blue wire.
All legs tested within 1 volt of ea. other (214V) from leg to leg.
123V from leg to ground.
Time to turn my attention to the mill.