I recently acquired this Thermoline/Temco heat treat oven.
I decided to rebuild the control system to ensure it was up to snuff. I installed a Inkbird PID (With ramp/soak functions), dual 25 amp SSRs, K-Type thermocouple and all new wiring from scratch. The oven cost me $300 and I have another $100 in parts in it so not a bad deal! It took 2-3 hours to wire everything up and I was ready to fire it up. Then came the sparks! On first run it INSTANTLY burned out BOTH 25 amp SSRs, causing them to short to ground and blew a double 15 amp breaker, NOT COOL! (No people were harmed in the making of this disaster)
I have been through the wiring and have not found any miss-steps, so I started checking the elements (the only real load). I ohmed them out and got 3.8 Ohms combined (or 1.8 and 1.9 ohms each) as they are in series. That didn't seem bad until I did the math volts/ohms = amps or 220/3.8 = 57.89 AMPS !?!?!? The data plate says 17 amps! Have my elements gone bad (how?) or am I making some dumb mistake?
I decided to rebuild the control system to ensure it was up to snuff. I installed a Inkbird PID (With ramp/soak functions), dual 25 amp SSRs, K-Type thermocouple and all new wiring from scratch. The oven cost me $300 and I have another $100 in parts in it so not a bad deal! It took 2-3 hours to wire everything up and I was ready to fire it up. Then came the sparks! On first run it INSTANTLY burned out BOTH 25 amp SSRs, causing them to short to ground and blew a double 15 amp breaker, NOT COOL! (No people were harmed in the making of this disaster)
I have been through the wiring and have not found any miss-steps, so I started checking the elements (the only real load). I ohmed them out and got 3.8 Ohms combined (or 1.8 and 1.9 ohms each) as they are in series. That didn't seem bad until I did the math volts/ohms = amps or 220/3.8 = 57.89 AMPS !?!?!? The data plate says 17 amps! Have my elements gone bad (how?) or am I making some dumb mistake?