- Joined
- Jun 12, 2014
- Messages
- 5,127
The ground is wired fine, on the connections to the VFD it is difficult to see from the picture. If this is a single phase VFD (WJ200-015SF), then power (240VAC) comes in and connects to the input power L1 and N, the motor connections are U/T1, V/T2 and W/T3. The power transformer power would connect to L1 and N terminals, or the main power system switch. Nothing but the motor should be connected to the motor output terminals of the VFD. I am assuming you have a 3 phase motor, it makes no difference for the contactors/transformers if this was a single phase or 3 phase version.