Since these are only carrying signals, the wire does not need to carry any significant current, and due to both size and cost restrictions it should be reasonably small. It needs to have six conductors. does not need shielding, and should probably be between 20 and 24 AWG. It can be either stranded or solid. Since the signals are going to be 230VAC, 60Hz, the cable need to be rated for 600VDC. I have been looking around, but all I can find is either high current (16AWG or more) or only rated for 300VDC.
How about selecting the size wire you require in single strands then after you run them wrap them with spiral wire loom wrap which come in numerous sizes? it will make adding additional strands and replacing individual strands easier...I am doing some 230VAC signal wiring on my mill, but I can't find any suitable wire. Since these are only carrying signals, the wire does not need to carry any significant current, and due to both size and cost restrictions it should be reasonably small. It needs to have six conductors. does not need shielding, and should probably be between 20 and 24 AWG. It can be either stranded or solid. Since the signals are going to be 230VAC, 60Hz, the cable need to be rated for 600VDC. I have been looking around, but all I can find is either high current (16AWG or more) or only rated for 300VDC. I need about 10 feet total length. I could possibly use individual multi-colored wires, but a single six-core cable is much preferred. PVC insulation is fine.
As good as I can explain in layman's terms.......Why would it be a problem to use 300 volt insulation on a wire carrying 230 volts?
I am well aware. I am not sure I have the room. The pathway is pretty tight. That. and of course doubling up on the color code - especially with 230V - is not exactly ideal.230V is unusually high, 24V or 12V is much more common for signal. McMaster has 600v, 18ga 6 conductor at around $4 a foot. Not sure you can get it any cheaper, maybe try a surplus vendor. Could you possibly run 2 @ 3 conductors? That you might find much cheaper as its way more common.
Exactly, and 325V is not merely close to 300V, it is higher. Add in surges, and the voltage on a 230VAC line can readily exceed 400V from time to time, and 230VAC is nothing to play around with.As good as I can explain in layman's terms.......
When talking about AC voltage the listed voltage is the average voltage.
With AC the voltage starts at 0V and rises to a value greater than the rated voltage, so that the average comes out to the rated voltage.
In this case it is 230V AC. that means the peak voltage will be 325.3 volts. This would exceed the rating of the 300V wire. Everything in the system must be rated to handle more than the 325.2V. It is bad practice to design real close to the design limits, you always want some safety factor.
To get the peak voltage you multiply the rated voltage by the square root of 2 (1.414)
Thanks!A 6 conductor is not common, either 5 or 7. The key word is 600V rating, and although this may be control wiring the gauge should be in accordance with the fuse rating for the wiring, as a short circuit could cause the wire/insulation to go up in smoke very quickly. Automation direct has 20AWG and 22AWG on 600/1000V rating at around a $1-2/foot, 20'minimum. Free shipping on orders over $50. Ebay listing below is for 10' 600V for $14 shipped.
SAB 02042007 20 AWG 7C Flexible PVC Control Cable LOT OF 10' FOOT | eBay
If you are not able to pick up locally, we are able to get competitive freight quotes as well.www.ebay.com
It is usually rated for 300V. Certainly all that I have is. Playing pattycakes with insulation rating is bad enough, but doing so with tightly twisted pairs... No, thank you.If it is in fact signal wire CAT6/CAT6A Ethernet cable comes to mind. You can get solid or stranded and 8 distinct conductors color coded for a very inexpensive price. Depending on use and mfr it comes in 16 - 23 AWG sizes.
600V ribbon cable?Ribbon cable comes to mind. You can get it in multicolor to make it easy to hand-wire stuff. It's easy to split so if all you find is 10-conductor or the like, just split off what you don't need.
It isn't, and yes, it is an unusual case.Must be an unusual case- signal lines are rarely more than 24 v
If it's for VFD signalling