The switch arrived via DHL at 8 pm Thursday.
This morning, I got the switch ohmed out and found that the coil is connected between terminal 8 and A1 although the drawing on the switch shows the coil between 4 and A1. Coil resistance is 889 ohms.
Terminal 4 is the 120-vac side.
Terminal 8 is the neutral connection.
So, 120-vac fed from the supply on the board, (Shown in red) thru the F/R switch then to A1, then thru the coil and to neutral. Solenoid energizes.
The only problem I have with this set up is that to break the 120-vac you have to forcibly pull the solenoid flapper away from the solenoid with the red stop PB.
I opened a bad sw. and that is the way it works.
I really do not understand the logic in this procedure as forcibly pulling the actuator away from the solenoid is asking for a burned-out coil.
I installed a small Normally Closed stop PB in series with the supply 120-vac to electrically drop out the coil.
No more forcing.
I am ready to roll.