It seem that grounding the pot case is capacitively coupling the resistor to gnd. The leakage current will be insignificant through the DC path if your 20 meg measurements from pot case to wiper and resistor ends is accurate.
It would be interesting to squeeze one lead of a 0.01 µF or 0.10 µF (not electrolytic) capacitor under the pot nut and washer. Then connect the other end to the housing with the pot floating in space and see if the behavior repeats.
Tripping the CFGI is troubling. Something is causing current to flow through the supply gnd wire. Check the resistance of the armature connections to actual gnd. Do the same with the field.
Just for S&G's, try swapping the L1 and L2 connections on the drive board and retest.
Try connecting a gnd wire to the pot as described in the capacitor test, but make a home run connection to gnd and retest.
Look between the heatsink and the bottom of the drive PCB for metal chips or anything that could be providing a path to gnd.
Verify that the neutral and gnd are connected properly to plug that goes to the wall outlet.
It would be interesting to squeeze one lead of a 0.01 µF or 0.10 µF (not electrolytic) capacitor under the pot nut and washer. Then connect the other end to the housing with the pot floating in space and see if the behavior repeats.
Tripping the CFGI is troubling. Something is causing current to flow through the supply gnd wire. Check the resistance of the armature connections to actual gnd. Do the same with the field.
Just for S&G's, try swapping the L1 and L2 connections on the drive board and retest.
Try connecting a gnd wire to the pot as described in the capacitor test, but make a home run connection to gnd and retest.
Look between the heatsink and the bottom of the drive PCB for metal chips or anything that could be providing a path to gnd.
Verify that the neutral and gnd are connected properly to plug that goes to the wall outlet.