No need to wonder... yes, it will fit in 3/4" conduit.I came up with 40% fill (this is assuming you are using THHN). Note that 6 current carrying conductors require you derate to 80%, but since that is based on the 90C limits, you are still good with your planned wire size. YMMV, since Canada has sometimes stricter codes.
http://www.electrician2.com/calculators/rf_calculator.html
You could also make your life easier, and surface mount a small breaker panel near where your tools are, and just run 8AWG to that panel. Easy to turn power on to the machines. Wish I thought of that before I ran 10AWG for each circuit 75' across my garage in the attic.
That calculator is pretty cool, I usually just cut a small section of pipe and stuff it with wires and use my eyetrometer to measure it, no inspection so the 40% fill is negotiable as we are only using low voltage at work but with 220 with high loads it's nice to be safe.
Really like the idea of running a small sub panel over by the machines, that would be a nice set up.
I'll check what wiring we have in stock and then decide, probably don't have 8 but good chance we have a few partial rolls of 10 and 12 left over from jobs, need to think about that.
I went up in the ceiling today to see if I could feed a wire up over the suite and back down into one of the other hatches, no go they are all separated so it will require surface conduit for 65' or so.
That will be a nice job for my oldest son as he has been working on one of our crews for the last year and is apparently really good at bending and installing pipe, not a complicated install but he can go in the attic as well and save me from getting hot and bothered up there.
I'll stub down off a box in the attic and use a LB Pull connector on the ceiling rather than another box, it should look pretty discrete and then run across the ceiling.