On the start up - Tell the Misses it just takes a bit of time but it'll all work out. This should work and it's a very sophisticated device. I've been nearly in fits and tears at times. Tell her one of my Fav. quote scenarios: "Experience is a tough teacher. You get the test first, and the lessons later". It'll run! I've started to get things together pretty well as time has gone on.
A few things: #1 can we revisit your Motors input VAc setting? Is it possibly wired for 220 -vs- 380? This is usually something you setup w/ jumper bars under the lid where the wires go in. A jumper Config for 220 3 phase input or a jumper config for the 380 3 phase. I am wondering is this is set to the 220 3phase under the motor's hood. Which would lead us to swap around your settings back on a few PD values. ... Or was that already confirmed in the threads? If set wrong the Current and Voltage curves will be all off and it will pop the error codes and stop.
The 4 poles note is also important. The Poles setting is found on page 54 PD143. should be 4 (default) And maybe check these too pls.
PD141 rated motor Vac. (when you find out if 220 or 380 hard wired for the input )
PD142 rated current of motor
PD144 Motor RPMS
PD14 can slowly be increased for torque.... default of 2% but goto 3 , 4 , or even 5% (After you determine what the motor is wired for).
On the bottom of page 28 of my manual, there is a small chart which outlines some code defaults for P009,10,14,15,41 Your model is on the top line.