The clouds are starting to part for me. The biggest concept shift is to get away from measuring the potential from ground.
Agreed, this is where a lot of the confusion comes from. But know that if you start expressing voltage measurements referenced to anything other than ground, you're going to upset a lot of people whose entire grasp of electricity is built on a foundation of the sacred reference point.
I seems that the neutral point for 3 phase is above ground potential.
Eh, not really, or at least it shouldn't be. I think you are still trapped in the ground-referenced mindset even though you've recognized the trap and are trying to break free. Maybe you have defaulted to a neutral-based mindset which is functionally the same thing. You need to bust completely out of the box for the epiphany to fully materialize.
Think about it this way: Let's measure the output of a 240V 3 phase Delta isolation transformer.
You measure from L1 to ground, you get nothing. It is ungrounded. There is no ground.
You measure from L1 to neutr... wait, there's no neutral either.
So, does this transformer then have no voltage?
Yes, it does, measure from (L1 to L2) and (L1 to L3) and (L2 to L3) and you will see 240V each time.
If you have an oscilloscope
with differential isolated probes, you can even look at the 3 waveforms (L1 to L2) and (L1 to L3) and (L2 to L3) simultaneously and see that they are 120 degrees out of phase with each other.
If you have an oscilloscope
without differential isolated probes, you can still look at the 3 waveforms (L1 to L2) and (L1 to L3) and (L2 to L3), but not simultaneously. You'll only be able to look at two phases at a time.
Once you've got your head wrapped around that 3 phase delta Isolation transformer with no neutral and no ground, let's perform some unsanctioned modifications to that mental model of a transformer. Open the cover, choose one of the phase windings, and right in the middle of it, scratch off the enamel and solder a wire onto it. You can name the wire. You can call it Bob, Winston, neutral, whatever you like. Most people would name it neutral. I'm going to choose the phase between L1 and L2, install my wire, and name the wire Ronald. Now I can measure from Ron to L1, and see 120V. Ron to L2, also 120V. Ron to L3, 208V? What the heck? Where did that oddball come from? Here's a hint: this is just geometry. You don't need to know the electrical formulas for polyphase power, you can get these numbers by sketching triangles in CAD.
The black lines are the phase windings. The blue measurement line is the 208V measurement.
The effect of our modification is that now we can use that center tap (Ron) to connect 120V loads.
There is no voltage between any of these points and ground, because this is still an isolation transformer. L1 to ground: nothing. Ron to ground: zilch. L3 to ground: nada. L2 to ground, nope.
Now let's connect Ron to ground. We have just made the center grounded delta distribution transformer (AKA high leg delta AKA wild leg delta) that many are familiar with . And since we are playing on the public court now, let's use house rules and rename Ron to Neutral.
If you measure between neutral and ground, you should not measure any voltage because they are connected together and should be at the same potential.
That high-leg delta is what is being generated by a RPC. We feed it this:
which is a
single phase, already center-grounded, and it adds the third leg (notice I didn't say "it adds the third phase" - because it actually add
two phases) to form the triangle above. That's why the graph on the first page of this thread shows the generated leg being so much bigger than the other two. It really isn't; the voltage output from a RPC on (L1 to L2) and (L1 to L3) and (L2 to L3) should each be 240V as expected, but it just
looks like a "wild leg"
when you use neutral or ground as a reference point instead of (L1 to L2) and (L1 to L3) and (L2 to L3), which makes more sense but most people aren't in the habit of doing it.
P.s. Instead of connecting Ron to ground, we could have connected L1 or L2 or L3 to ground, and then we would have had a corner grounded Delta distribution transformer (with a highly irregular center-tapped winding).
Ever measured a 480V circuit to ground? did you get around 277V? If so, it's because that's a WYE circuit and the geometry works for those too:
Again the black lines are the phase windings. The blue lines forming the triangle are the the 480V measurements.
While we're doing thought experiments, let's modify that 480V transformer above. Let's delete that center neutral. We can't actually delete the node where the phase windings are connected together, but we can cut the neutral wire and ground wire off, turning it into an isolation transformer so that no ground-referenced measurements are possible, and no neutral-referenced measurements are possible.
Can we still measure the output? Yes! From (L1 to L2) and (L1 to L3) and (L2 to L3).
We still have 480V 3 phase power available even in the absence of the holy reference point!