I have no idea what design you are using, the basic install uses the contactors and the stock AC transformer. You cannot mix power for the relay controls with the VFD inputs on the relay designs I have done, not sure why you would want to do that since the VFD has its own internal power supply. I have done designs for other VFD's that use a single supply, but there are issues of electrical noise and voltage spikes from the relays that could damage the VFD inputs. I did one build that way and designed subsequent systems keeping everything separate. A 10W 24VDC power supply is pretty marginal, depends on the design but I usually use 65-100W. The system current draw with small relays and if I using a coolant contactor is around 500 mA 24VDC. On smaller builds I will use a step down converter to get 12VDC, otherwise I use two separate power supplies.
E-Stop is different then turning off the power, in one case you want to kill the run commands to the VFD and issue a fast stop, depends on the VFD and the control design. In some cases people choose to have it shut down the output section of the VFD (safe torque off), etc..
E-Stop is different then turning off the power, in one case you want to kill the run commands to the VFD and issue a fast stop, depends on the VFD and the control design. In some cases people choose to have it shut down the output section of the VFD (safe torque off), etc..