Not for a VFD. The vfd is for my mill.I am unclear as to what the brake wire is connected to, it sounds like it connects to the brake microswitch but you do not indicate what it is connected to or used for. If to a VFD low voltage input, then it is usually 24VDC and a few mA so only needs to be control cable 18 to 22awg wire, if to a contactor then the voltage rating of the contactor and current of the fuse so 16 to 18awg. If you are talking external braking resistor than minimum 400vdc at several amps so 600vac or vdc rated and 14awg for up to 3hp vfd 220vac rated.