Several things illegal under Oregon State law with this post due to the dangerous conditions created, please do not duplicate this information.
see 210.21, 404.3, 404.14.
edited 404.21 to the correct requirement of 404.14
After reviewing the cited sections, I have to agree, you are correct. Thank you.
210.21, to be in compliance I would need to add the proper supplementary protection at my ''power strip'', or simply exchange the 30 amp panel breaker for a 20 amp panel breaker since all of the receptacles are rated for 20 amps, Table 210.21(B)(3). The total connected load is well within the Table 210.21(B)(2) ratings.
404.3 seems to be in compliance.
404.14 (B)(1) and (B) (2) seem to apply and are in compliance.
404.14 (E) may not be in compliance, at least using the connected hardware since it's rated for tungsten lighting loads, however a Nichrome load is electrically nearly identical, having a lower inrush.
404.14 (F) does not seem to apply because the switch is downstream of the receptacle.
However, I would submit that all of the hardware downstream of the receptacle is in fact a portable heating appliance and thus Section 404 does not apply at all. If this were installed as a permanent installation then it would absolutely be out of compliance.
I'll edit my original post to reflect this.