Running 208v motor on 220v service

Discussion in 'ELECTRICAL ISSUES - POWER YOUR MACHINES & SHOP' started by toolman_ar, Jun 1, 2017.

  1. toolman_ar

    toolman_ar United States Active User H-M Supporter-Premium

    Likes Received:
    39
    Trophy Points:
    28
    City:
    Birmingham
    State:
    Alabama

    -Return to Top-

    IMG_3982.JPG I am looking at a grinder and have a question regarding the power requirements.

    I have a 2hp Ronk phase converter. It produces 220v, 3 phase power.

    The grinder is 3 phase, 208v, 2hp, 5.76 amps.

    Do I need to reduce voltage to the grinder to run with my phase converter?

    Toolman_ar
     
  2. JimDawson

    JimDawson Global Moderator Staff Member Director

    Likes Received:
    3,783
    Trophy Points:
    113
    City:
    Sandy
    State:
    Oregon

    -Return to Top-

    That one is a tough call. Most newer motors will run 208-240 just fine. If your phase converter is actually putting out 220V you should be fine, but I suspect if your power is anything like mine, you will be closer to 240V. I would wire it up and put an amp probe on it, if the current draw is within reason, you should be fine. The motor insulation is good for at least 600V, probably more.
     
    Chipper5783 likes this.
  3. toolman_ar

    toolman_ar United States Active User H-M Supporter-Premium

    Likes Received:
    39
    Trophy Points:
    28
    City:
    Birmingham
    State:
    Alabama

    -Return to Top-

    Jim,
    After I wrote 220v, I thought I need to go look to confirm. I have not checked, but think you are correct, most likely 240v.

    This grinder is most likely bigger than I need. The seller has not confirmed the wheel size. Just trying to do my homework. Before dragging home something I cannot use.

    toolman_ar
     
  4. JimDawson

    JimDawson Global Moderator Staff Member Director

    Likes Received:
    3,783
    Trophy Points:
    113
    City:
    Sandy
    State:
    Oregon

    -Return to Top-

    I just checked my voltage for today, low volts 241.2 at 10:00 PM, high volts 245.2 at 7:20 AM. I suspect you will be fine anyway, but it would suck to have to install buck transformers.

    You might check with your local motor shop for an opinion.
     
  5. Ulma Doctor

    Ulma Doctor Infinitely Curious Active Member

    Likes Received:
    2,718
    Trophy Points:
    113
    Location:
    Ethereal Plane
    City:
    Tracy
    State:
    California

    -Return to Top-

    generally speaking, if the nameplate voltage is within 10% of supply voltage, you'll be just fine :)
    for example 240v service - 24v(10%)= 216v
    216 is 8v higher than 10%, it should cause no real problems.
    the amp draw will be less than nameplate amps @240v
     
    Rustrp and JimDawson like this.
  6. JimDawson

    JimDawson Global Moderator Staff Member Director

    Likes Received:
    3,783
    Trophy Points:
    113
    City:
    Sandy
    State:
    Oregon

    -Return to Top-

    Mike, I was hoping you would chime in here. :) so running a 208 volt motor on 240 volts the amp draw will actually be lower than nameplate?
     
    Rustrp and Ulma Doctor like this.
  7. toolman_ar

    toolman_ar United States Active User H-M Supporter-Premium

    Likes Received:
    39
    Trophy Points:
    28
    City:
    Birmingham
    State:
    Alabama

    -Return to Top-

    The neet thing about this grinder is that the manufacturer, The United States Electrical Tool Company is still in business.

    Tomorrow I will contact the manufacturer and ask what they think. Also it looks like I can provide them the serial number and they can date the machine.

    The web site shows the Modle 500, is offered in 240/440.

    toolman_ar
     
    Rustrp likes this.
  8. Chipper5783

    Chipper5783 Active User H-M Supporter-Premium

    Likes Received:
    343
    Trophy Points:
    63
    City:
    Red Deer
    State:
    Alberta

    -Return to Top-

    240 volts on a 208V motor? Not an issue. As, others have pointed out - check that the current draw does not exceed the name plate value. Do you have a clip on current meter? Even a cheap one would be adequate.
     
    Ulma Doctor likes this.
  9. Ulma Doctor

    Ulma Doctor Infinitely Curious Active Member

    Likes Received:
    2,718
    Trophy Points:
    113
    Location:
    Ethereal Plane
    City:
    Tracy
    State:
    California

    -Return to Top-

    Yes Sir Jim,
    we know from Ohm's Law, (if the resistance is kept constant)
    the voltage in a circuit increases- the Amperage will decrease
     
    Rustrp and JimDawson like this.
  10. markba633csi

    markba633csi United States Active Member Active Member

    Likes Received:
    314
    Trophy Points:
    63
    City:
    Mountain View
    State:
    California

    -Return to Top-

    That's true for transformers but not for resistive loads Mike. V over R equals I. Increase V and you will increase I.
    Mark S.
    ps there may be some goofy inductive effect that makes the current go lower, I don't know
     
    JimDawson likes this.
  11. toolman_ar

    toolman_ar United States Active User H-M Supporter-Premium

    Likes Received:
    39
    Trophy Points:
    28
    City:
    Birmingham
    State:
    Alabama

    -Return to Top-

    Turns out US Electrical Tool is out of business. The plant auction was 4/17/2017. Makes me sad to see an old company like this fold.

    Thank you for your advise on the Electrical question!

    toolman_ar
     
    Rustrp likes this.
  12. Rustrp

    Rustrp United States Active Member Active Member

    Likes Received:
    437
    Trophy Points:
    63
    City:
    Sacramento
    State:
    California

    -Return to Top-

    I think you will be good on the voltage difference, and especially when you consider the possibility the motor hasn't seen 208v in it's lifetime. It's close to the allowable guidelines.
     
  13. 4gsr

    4gsr Global Moderator Staff Member H-M Supporter-Premium

    Likes Received:
    2,101
    Trophy Points:
    113
    Location:
    Victoria, Texas
    City:
    Victoria
    State:
    Texas

    -Return to Top-

    Oh yeah, should work fine. I ran a 2 HP 208 volt motor on a home made static converter 40 years ago. Motor never got hot. Go for it!
     
    Rustrp likes this.
  14. Ulma Doctor

    Ulma Doctor Infinitely Curious Active Member

    Likes Received:
    2,718
    Trophy Points:
    113
    Location:
    Ethereal Plane
    City:
    Tracy
    State:
    California

    -Return to Top-

    Ohm's law holds for circuits containing only resistive elements (no capacitances or inductances) for all forms of driving voltage or current, regardless of whether the driving voltage or current is constant (DC) or time-varying such as AC. At any instant of time Ohm's law is valid for such circuits.
     
    4gsr and JimDawson like this.
  15. talvare

    talvare United States Ted A H-M Supporter-Premium

    Likes Received:
    320
    Trophy Points:
    63
    City:
    Sacramento
    State:
    California

    -Return to Top-

    The formula for three phase motor electrical calculations is : I= HP x 746 / 1.73 x E x Eff x Pf. Since the motor data plate doesn't indicate an efficiency rating or power factor we can only calculate a simple theoretical amperage rating. Amperage (I) at 240V = 3.6. Amperage at 208V = 4.14 . This validates Mike's voltage/current relationship.

    Ted
     
    4gsr, hman, Ulma Doctor and 2 others like this.
  16. markba633csi

    markba633csi United States Active Member Active Member

    Likes Received:
    314
    Trophy Points:
    63
    City:
    Mountain View
    State:
    California

    -Return to Top-

    Yep just as I suspected, that darn high-falutin' math strikes again!
    MS
     
    Ulma Doctor likes this.