White wrapped wire goes to neutral, not to ground or earth which are the same thing and where the green wire is going.
So based on this you need to pull one more large black wire of the same guage as the others through the conduit and tape it blue at both ends.
Now, is the unused three pole breaker that was tagged as "garage" 100 amp as well? If so run all three wires to that one, otherwise replace it with a 100 Amp breaker and use that.
So that gets you 3 phase to the garage.
Next step is to determine if the panel in the garage is a three phase panel or just a single phase panel. If three phase, add the new blue wire and you are set, otherwise, you will need to replace the panel.
Basicly Ron, you have been stewing over something you already had.
Walter