- Feb 1, 2015
- 9,607
My understanding of a GFIC is that it senses an imbalance between the current on the load line and the neutral line. An imbalance is interpreted and leakage to ground, whether at the ground terminal or through an external path, and it trips the GFIC. It doesn't look at a voltage difference between the ground and neutral lines. Normally, there will be a small difference between the voltage on the neutral line and the ground line because normally, the ground line carries no current but the neutral line does. because it does, there will be a IR voltage difference due to the resistance of the wire.
A high resistance short can occur in a device which can bring a voltage to a point where a person could contact it. An example would be a portable tool left out in cold weather and brought into a warm environment. Condensation would occur and could provide a path for voltage to reach the case of the tool. A GFIC will trip on a few milliamp imbalance, not enough to trip a breaker but but sufficient to prevent a person from a lethal shock.
A three wire circuit, (load neutral, ground) with properly grounded appliances or machines should not need a GFIC as there is no possibility of personal contact with an exposed voltage. Double insulated appliances with two terminal connections can fault to the point where a person is in contact with a dangerous voltage and if also in contact with an external ground. a potentially lethal situation could arise.