At work we have a larger version of that style of box.
http://www.brownells.com/gunsmith-t...extra-large-heat-treat-furnace-prod13791.aspx
Internal size of about 22x22x13". Takes a long time to heat up due all the thermal mass involved. I have it on a timer so that starts on the early morning before we get in. I replaced the analog controls with Watlow PWM controllers. Added 2 thermal couples, one for the main control and the second for over heat protection.
Yes the temperature will vary based upon position. Every one is different. Difficult to test without a bit of work and charting it all on paper. Using a temperature probe that you can bend a bit to reach at a minimum of 8 zones, 27 zones is better. Divide the space into 2 layers of 4, 3 layers of 9. Another way would be to use Temperature indicating paint on some test pieces and use some method to support them in the various zones.
As for protecting the heating elements from an early death, use a ramping program that does not run at 100% for any long length of time. PWM is a very good way to control the power going to the elements. We use a S&M Engineering belt annealler, we start it off at 1000 F, which it reaches fairly quickly. During the work week we leave it at 1000 24hrs as an idle temp. Naturally this would not work for you. A touch expensive. We go from there to what ever temp is required for the job. It is the 100% power setting that kills the elements. They will get stressed and burn out near the joints where the exterior wiring meets the elements. The other place they burn is if there is a sharp bend.
As for gas we use Nitrogen 5.0 or crack Ammonia for a 4/1 Nitrogen/Hydrogen mixture. Argon gets expensive in our case.
Pierre