I am new to the forum & will be greatfull for any info thanks.
I have just got a viceroy 11x24 lathe, with a 1.2 Hp motor 3ph & will be getting a VFD unit to run the motor.
reading this post & others i have got a lot of info on VFD's, not all ponting the same way.
1, a VFD with adv flux vecter control will develop nearly full torque at virtually any RPM.
but a std one will not, is a vector control a must. yes or no ????
2, is a IP65 (dri box) needed in a unheated room or garage (some say it is a must have) or will a IP20 (not a sealed box) be ok. Y/N
3, i was going to get a 3 Hp VFD for the 1.2 Hp motor, but may put a 3 Hp motor on, at a later date.
so do i get a 4 Hp VFD or not.
thankyou, great forum.
jeff
Jeff
Yes you want to stay with a Vector Drive VFD to get maximum preformance from it and your motor.
not sure about the box, but I would err on the side of caution. It is more a question of how likely will the box be to get wet, or condensation in it. If in doubt, protect it.
As for the size of VFD, if it is a newer VFD and it was designed as 3 Hp 220V single phase input, to 220V 3 phase output then you can use that VFD when you upgrade to the larger 3 HP motor. If the VFD is an older unit, or if it is not designed for 1 to 3 phase operation, then it must be dealt with differently. When VFD's were first designed, they were designed to vary the speed of motors in existing 3 phase circuits so they were to input 3 phase voltage, convert that to DC, then convert the DC back into 3 phase with a controllable varied frequency output which allowed the motor's speed to be changed. Now if this unit is only supplied with 1 phase then it has to be derated by 2/3 of it's rated output HP as it does not have the same amount of power being applied by leaving out the 3rd leg of the phases. With newer units the manufacturer has already taken this into account and rated the unit accordingly. Thus the fact that the VFD in my lathe is rated at 3 HP 3 Phase but only 2 HP 1 phase input and in order to use it as a phase converter, I would have to replace the VFD.
So in your case, you would have to use a 5 Hp VFD to operate a 3 HP motor, if it has not already been derated by the factory, or you can use a 3 Hp unit to control the 3 Hp motor if it is rated correctly for that application.
It is the same with my welding equipment. They are rated at 100 % duty cycle if they are run off of 3 phase power, but the duty cycle drops to 2/3 if they are powered by 1 phase.
Walter