Help Motor Identification FT1

Typical low voltage connection would be:
1-7 to L
2-8 to L
3-9 to L
4-5-6 tied together

High volt age would be:
1-L
2-L
3-L
4-7 tied together
5-8 "" " " "
6-9 "" " " "
This would seem to fall in line with what you have except for the lead markings.
 
I know someone that might be able to help, if you still have issues.
 
I don't have it figured out yet. I am going to contact Lagun tomorrow and see if I can talk to Carmen.
 
I don't have it figured out yet. I am going to contact Lagun tomorrow and see if I can talk to Carmen.
Not a bad idea. Have only talked/emailed him a few times, and he seems to be super knowledgeable, and happy to help.
 
Sorry I can't be of help. My motor is a 3hp unit from a French company. It's long with cooling fins. Not the same.
 
It has been an awesome day. Carmen at Lagun was able to send me a diagram (attached) of the proper jumper configuration for 240v. It was jumped for 440v. Mill is up and running and my VFD no longer gives me line fault errors. Thanks to all who contributed.
 

Attachments

  • FTV motor Volts Change.pdf
    90.3 KB · Views: 3
Outstanding! I'm surprised by how many different motors Lagun used. Mine is a 3hp frenchie, tall with cooling fins. Wouldn't have been helpful to you. Congrats on keeping another Lagun alive.
 