Messy set of questions coming up. If you make it to the end, thanks for sticking with me on this, reading and providing some insight.
I'm gearing up to design and build a CNC lathe. The not so obvious reason for this is that I desire to have a fast, accurate gang tool style lathe that can handle C-axis style "plane switching". This means that the machine can mill using the spindle as an axis in combination with live tooling. If you are unclear on what I'm referring to, lookup Omniturn GT-75 lathes. Yes, it is ambitious and yes, I'm already in over my head. Jim Dawson has provided some great advice on planning and servo drive and motor selection.
I'm already in deep. I've purchased an XZ stage from a used Omniturn. Everything is NICE and solid, tight and in great condition. It was used to produce pool cues so very little abuse. I have 750W servos and DYN4 drives for the stage. I'm using the Centroid Acorn controller which supports C-axis control. I have Hardinge HC headstock with 5C spindle and the 7" dovetail bed. I've purchased all of my steel for the frame build. I'm committed.
OK, now my problem. Electrical worries. My shop has a 60A subpanel coming off the main 200A inside the house. For the sake of discussion, call it a 75ft. run through the basement, underground conduit and into the shop.
When I talked to the folks at DMM, they suggested the recommended sizes for circuit breakers is 20A for each of the XZ servo drives and 30A for the spindle servo drive. They also suggested that I could just combine it all into one breaker. That is a 70A breaker.
Time for me to panic?
Here are the rated currents for the DMM servo drives:
I have two of the H01 and will have one of the T01 for the 1.8kW spindle servo.
Here is the basic diagram with their recommendations on circuit protection and signal filters:
Here is the 1.8kW servo motor specs that gets paired up with the DYN4-T01:
And the specs for the 750W motors that get paired up with the DYN4-H01:
Hopefully you can see my confusion. I'm under the distinct impression that the motor protection is clearly for the servo drives. The drives must be doing some sort of inrush current management to the motors because the breakers are not sized to cover the max. rated current for the motors. It seems to me that the MCCB recommendations are overkill for the servo drives. I would think that a more appropriate size for the MCCB would be one 40A based on the rated current for those three drives. Mind you, this is a guess on my account. Not a calculated educated guess, but just a guess on loose experience. What say you?
Before you weigh in, now for my unpleasant surprise. As I was researching all of this, the question popped into my mind about what my current feeder conductor is. I stepped into the basement and located my run from the main panel making it's way over to the garage. It looks like I have a 60A run with 10AWG feeding the shop. While 10AWG can handle 60A based on what I researched, it also seems there is some question that it can't handle the 3% voltage drop tolerance for a run pushing 75-100ft. Do I already need to upgrade my service before I move forward?
Ideally, I'd like to run this machine off a 40A, 1Ph, 240V branch circuit coming out of the sub panel. I will likely have a coolant pump at some point and possibly other accessories like lighting but I'm not too worried about those. My biggest concern is safety of the main circuit. I don't want a fire and don't want to smoke a drive.
Any thoughts or questions that will help me resolve this? Am I worried about something I don't completely understand?
Thanks all.
Bryan
I'm gearing up to design and build a CNC lathe. The not so obvious reason for this is that I desire to have a fast, accurate gang tool style lathe that can handle C-axis style "plane switching". This means that the machine can mill using the spindle as an axis in combination with live tooling. If you are unclear on what I'm referring to, lookup Omniturn GT-75 lathes. Yes, it is ambitious and yes, I'm already in over my head. Jim Dawson has provided some great advice on planning and servo drive and motor selection.
I'm already in deep. I've purchased an XZ stage from a used Omniturn. Everything is NICE and solid, tight and in great condition. It was used to produce pool cues so very little abuse. I have 750W servos and DYN4 drives for the stage. I'm using the Centroid Acorn controller which supports C-axis control. I have Hardinge HC headstock with 5C spindle and the 7" dovetail bed. I've purchased all of my steel for the frame build. I'm committed.
OK, now my problem. Electrical worries. My shop has a 60A subpanel coming off the main 200A inside the house. For the sake of discussion, call it a 75ft. run through the basement, underground conduit and into the shop.
When I talked to the folks at DMM, they suggested the recommended sizes for circuit breakers is 20A for each of the XZ servo drives and 30A for the spindle servo drive. They also suggested that I could just combine it all into one breaker. That is a 70A breaker.
Time for me to panic?
Here are the rated currents for the DMM servo drives:
I have two of the H01 and will have one of the T01 for the 1.8kW spindle servo.
Here is the basic diagram with their recommendations on circuit protection and signal filters:
Here is the 1.8kW servo motor specs that gets paired up with the DYN4-T01:
And the specs for the 750W motors that get paired up with the DYN4-H01:
Hopefully you can see my confusion. I'm under the distinct impression that the motor protection is clearly for the servo drives. The drives must be doing some sort of inrush current management to the motors because the breakers are not sized to cover the max. rated current for the motors. It seems to me that the MCCB recommendations are overkill for the servo drives. I would think that a more appropriate size for the MCCB would be one 40A based on the rated current for those three drives. Mind you, this is a guess on my account. Not a calculated educated guess, but just a guess on loose experience. What say you?
Before you weigh in, now for my unpleasant surprise. As I was researching all of this, the question popped into my mind about what my current feeder conductor is. I stepped into the basement and located my run from the main panel making it's way over to the garage. It looks like I have a 60A run with 10AWG feeding the shop. While 10AWG can handle 60A based on what I researched, it also seems there is some question that it can't handle the 3% voltage drop tolerance for a run pushing 75-100ft. Do I already need to upgrade my service before I move forward?
Ideally, I'd like to run this machine off a 40A, 1Ph, 240V branch circuit coming out of the sub panel. I will likely have a coolant pump at some point and possibly other accessories like lighting but I'm not too worried about those. My biggest concern is safety of the main circuit. I don't want a fire and don't want to smoke a drive.
Any thoughts or questions that will help me resolve this? Am I worried about something I don't completely understand?
Thanks all.
Bryan