I am quite familiar with the VFD's and specific with those from Acra/Sunmaster. Please post a picture of the current VFD installed from the factory so I can give you further details. A DC choke is recommended for single phase input on a 3 phase input VFD used in derated mode. This can usually be fitted in the electrical cabinet on the base. In general for a 3 phase input VFD, I use the same size fuse as would be used for 3 phase input as I do for single phase input in a derated mode. When I know the VFD model I can give you specifics on both. You do not need to change any of the programming on the VFD, it should remain the same if you do not change the VFD. If you do change the VFD to the V1000 I can provide some guidance as to programming but we would need to pull the programming parameters from the current VFD. The V1000 uses a special cable to program it via computer, and a serial to USB adapter.
The input wiring does not change, I would use the current fuses already in place. The previous Acra models were oversized (7.5Hp) continuous duty VFD's for a 5 Hp motor, but it seems like there was a change recently as I also encountered this with someone else. The alternative is to run it off of an RPC or Phase Perfect.
Provide me with the model number of the G7 that is the default VFD.
The input wiring does not change, I would use the current fuses already in place. The previous Acra models were oversized (7.5Hp) continuous duty VFD's for a 5 Hp motor, but it seems like there was a change recently as I also encountered this with someone else. The alternative is to run it off of an RPC or Phase Perfect.
Provide me with the model number of the G7 that is the default VFD.