Thanks! You are right. I ignored the fact that the neutral is not used and it is only 2 floating legs so it is easy to create a 3rd leg that has the proper phase relationship.What you are considering is where the neutral is referenced to. In standard three phase, the neutral is often considered to be the center of the triangle. So 120 degrees between legs relative to neutral. In high leg delta 3 phase (google it for pictures), the neutral is the center of one side of the triangle. So two legs are 180 and one is 90 from neutral, but it is still an equal lateral triangle, 240 volts between any two legs. 3 phase motors don’t use neutral, so they don’t care what neutral is referenced to. RPCs produce 3 leg delta, which is why you measure line to line voltage but get funky results for line to neutral.
Three leg delta is also fairly common in industrial use. It delivers the classic 3 phase, plus 240v and 120v single phase. Otherwise you get 3 phase with 208V leg to leg and 120V leg to center of the triangle neutral. A 240V 3 phase center to neutral would give something odd like 138V. At least I think that’s right, I’m doing geometry in my head so my math is not guaranteed.
The two legs of 120V are indeed 180 degrees out of phase. In my mind that is indeed two phases, described mathematically be two different angles, or two different vectors. But, they are generated by a center tapped transformer. On the high voltage side there is only one voltage, generating both 240 and/or splitting that into two sets of 120v. So power guys think of it as single phase. My background is more signal related so I would say its one phase of 240 or two phases of 120. This gets to be almost a religious argument, depending on background. Convention in nomenclature is to count phases on the powerline side.@rabler
Reading your reply, I realize I didn't ask the question well enough.
In your reply, when you say "You really can’t define an angle without two phases", does that mean the two hot (120V) legs of 240V single phase service are not "two phases"?
@Dabbler Not completely true. See the wikipedia article on high leg delta for another example. Admittedly this is a variation of the delta configuration, but it is an important difference when a site uses both single and three phase.In a delta 3phase system each of the two terminals make a single phase sine wave 240V RMS there are 3 ways to connect to a 3 phase source, and each of those sources are 120 degrees apart. In a Y 3 phase system each of the sources measure 208 volts RMS.
There is no other 'geometry' here.
oversimplifying to think those are the only configurations.
Yes, that should prevent you from being able to start the motors on many machines. But connecting controls to the derived leg is generally bad for two reasons: the derived leg is less well regulated and usually the controls are what are going to be more sensitive to the voltage fluctuation. Also, RPC's generally start better with no load on the generated leg, and the control circuits are the most likely to put a load on that leg with the end machine not fully on. I've retrofitted my three phase lathe with a bright indicator light across the controls leg to show that it is on so I know to throw it's internal disconnect switch, although my RPC is set up so that when it is off, all three legs are disconnected.I wondered what would happen if you forgot to turn the rotary phase converter on. Wouldn’t you be single phasing your three phase motor (and it would draw a lot of current)?
Perhaps if you connected one leg of the machines controls to the derived leg, then if that phase wasn’t present then either there would be no power available to the controls or the fuse of the controls would blow? (I don’t know what voltage the derived leg sits at when it’s not connected to the phase converter. It seems likely it will just float and can’t provide power?)
(Also, if the derived “neutral point” is not near zero, wouldn’t this also mean the insulation of the devices to ground needs to be higher too? And therefore the machines insulation voltage would also need to be confirmed?)
(I haven’t thought about this much since seeing the video(s (Oxtools and Keith Fenner), except for thinking I’d be very likely to forget to turn the rotary phase converter on eventually…)
that should prevent you from being able to start the motors on many machines.