Not true. Put a voltmeter across any two legs. You'll get rated voltage. Yes, the three legs are separated by 120 degrees phase angle, but the voltage is spec'd as the voltage between any two legs.The 3 legs of 3 phase current can be seen as 3 seperate sine waves 120 degrees apart. So 2 legs of a 3ph VFD will be 120 degrees apart resulting in under voltage across those 2 legs. So I would guess trying to control a single phase motor off of 2 legs from a 3ph VFD will not work very well.
I am correct. "The formula is volts times the square root of 3, which happens to be rounded off to 1.732. For 2 lines each carrying 120 volts, the calculation for this is 120 volts times 1.732, and the result is rounded up to 208 volts."Not true. Put a voltmeter across any two legs. You'll get rated voltage. Yes, the three legs are separated by 120 degrees phase angle, but the voltage is spec'd as the voltage between any two legs.
I am correct. "The formula is volts times the square root of 3, which happens to be rounded off to 1.732. For 2 lines each carrying 120 volts, the calculation for this is 120 volts times 1.732, and the result is rounded up to 208 volts."
Please read: https://www.raritan.com/landing/three-phase-power-explained
A VFD converts voltage in from AC to DC and then from DC back to AC, at just about any voltage the designer want. Often you can tweak the voltage within some range from nominal through the program settings. I happen to have a VFD that uses 120V single phase and generates 240V three phase for a small motor. See for example:240v single phase into a VFD will result in 208v output across any 2 legs of the generated 3 phase output.
220v single phase into a VFD will result in 190v output across any 2 legs of the generated 3 phase output.
Sorry you are wrong here:Mike,
I taught college level Electrical Engineering. While power systems wasn't my particular research area I'm familiar enough with the basics to be on firm ground.
That's voltage measured from neutral times the square root of 3. So three phase @ 120V to neutral will measure 208V between any two legs. You've picked an example but failed to realize that it is not the usual case. That is ONE possible three phase configuration. A three phase that measures 240V between each leg is a different, higher voltage, is more common, and is what most VFDs and three phase motors are built around, unless you get into the 440V class motors/vfds. This gets into the difference between delta and Y configurations, and is non-trivial.
The DC voltage from a single phase rectifier will be DC voltage = AC voltage divided by the square root of 2. Always! Rectifiers do not boost the output DC to any voltage you want. It is always AC voltage/1.4 for single phase AC.Totally wrong. A VFD converts voltage in from AC to DC and then from DC back to AC, at just about any voltage the designer want. Often you can tweak the voltage within some range from nominal through the program settings. I happen to have a VFD that uses 120V single phase and generates 240V three phase for a small motor. See for example: