How to wire "new" contactor to momentary switch

3
Like what you see?
Click here to donate to this forum and upgrade your account!
10

Reeltor

Active User
Active Member
Joined
Nov 18, 2014
Messages
737
Likes
308
#1
I need help wiring my shaper. Previous owner(s) cut and removed the contactor.
Here is what I have, a 16" G & E shaper with a 5hp 3-phase motor.
On the machine there is a momentary type push button on/off switch, the wiring appears to be in the main housing with the oil and gears (but I cannot see or get to where the wire enters the switch to replace it).
There is a Main Disconnect with 3-cartridge fuses (one for each phase), I have acquired a "newer" if not NOS contactor (or is this called a starter?) GE CL45

The push button switch on the shaper has 4-lugs, 1,2 &3 were used with #4 empty.

Photos of the parts are attached, what voltage is going to the switch? Normally, I wouldn't worry about it but the wiring exposed to the lube oil is a concern and I would prefer a low voltage on/off if possible. At this point I don't have a clue if the motor works, but it is a cool old motor and would like to keep it.

thanks,

Mike

GE CL45 face.JPG cl45 upper side A1-A2 connectors.JPG cl45 lower side A2 connector.JPG Westinghouse push button station.JPG push button leads 1-2-3, 4 empty.JPG shaper motor nameplate.JPG View attachment 237834 CL45 nameplate.JPG
 
Last edited:

jim18655

Active User
H-M Supporter-Premium Member
Joined
Nov 23, 2013
Messages
512
Likes
361
#2
Need the coil voltage of the starter.
Is there a transformer in the machine? (Probably not)
You need to find a 3 wire control diagram to follow the wiring.
Looks like a contactor only without overloads.
More to follow.
 

Reeltor

Active User
Active Member
Joined
Nov 18, 2014
Messages
737
Likes
308
#3
If there was a transformer on the machine it is long gone, there is a 110v transformer for a light circuit. I do have another old contactor, I'll shoot a photo or two of it. It might be a better choice.

Mike
 

jim18655

Active User
H-M Supporter-Premium Member
Joined
Nov 23, 2013
Messages
512
Likes
361
#4
Try to get a better picture of the full tag on the contactor above. I can't read it due to the glare.
 

British Steel

Active User
Active Member
Joined
May 12, 2011
Messages
691
Likes
523
#6
Hi Mike,

It looks like the plastic moulding between the A1 and A2 terminals bears the legend "208v 60 Hz" - if so that's your coil voltage and it would go across Neutral and one phase of the incoming 4-wire=plus-earth(ground) 3-phase, BUT what it doesn't have is an auxiliary contact to "latch" the contactor - the four slots on top are probably where additional aux' contact sets can mount.
What you will need for that contactor is a normally-open (NO) contact set to mount on top (probably manufacturer- and contactor-size-specific), then feed one 208v phase to one terminal of the contact set, onwards out to your green push-button (check it's push-to-make), wire other side of the push-button comes back and goes to A1 as does the other terminal of the NO contact set, then the A2 connects to neutral through a normally-closed (your red) pushbutton.

When you push the green NO button, it will apply 208v across the coil (the A1, A2 terminals), which will pull in the NO contacts and also operate the NO aux set, which will then maintain power to the coil and latch the contactor so you can let go of the button. When you push the red, it will break the coil's return to Neutral, no current will flow and the contactor will drop back put until you release the red and prod the green again - this will also give you no-volt-release, so if the power's lost the machine won't restart on its own, it'll wait for you to push the start button again :)

Ideally you should add a motor overload rated for the motor's full-load amps, between motor and contactor, and if that has an aux' contact set on it use that to break the neutral return if the overload trips, and it may be easier/quicker/cheaper to buy another contactor (EvilBay's good for this sort of thing) that already has the NO contact built in...

Hope that helps a little,
Dave H. (the other one)
 

British Steel

Active User
Active Member
Joined
May 12, 2011
Messages
691
Likes
523
#7
Oh, if you want to go low-voltage on the control circuit (a good idea, safer by a mile!), all the above applies, but put a 208-24v control transformer between incoming 208v and Neutral (with a fuse on the high voltage side!) and run the transformer's 24v output through the same way, using a contactor rated for your motor power with a 24vac coil.

Dave H. (the other one)
 

Reeltor

Active User
Active Member
Joined
Nov 18, 2014
Messages
737
Likes
308
#8
OK, the contactor that I have won't do the job.

If I go to eBay to look for what I need, what search terms should I use? I was able to wire up my RPC panel box to the lathe and mill without a problem but this (what I called a magnetic switch) is a first time for me.

here is an old contactor that I got with a craigslist purchase, it was connected to a 5-hp motor that I gave to a friend.
Is this something that can be used?
old contactor rotated.JPG
 

Ulma Doctor

Infinitely Curious
Active Member
Joined
Feb 2, 2013
Messages
4,298
Likes
3,495
#9
if you are serious about wanting to use the new 4 pole contactor listed in post 1 above, i can show you a latching circuit that uses momentary switches (1 NO start, and 1 NC stop)
if both the start and stop switches that are already present are NO for the start and NC for the stop- it will be a slam dunk
if your switches are somehow any different than NO and NC respectively, there is still hope- i just may need to modify the plan of attack

i'm sorry for the poor quality of the scan but i hope the idea lands...
(the overload and control fuses are omitted for simplicity)
latching circuit.jpg
 
Last edited:

killswitch505

H-M Supporter - Premium Member
H-M Supporter-Premium Member
Joined
Nov 10, 2013
Messages
187
Likes
142
#10
The problem with using the contactor in the picture you'll not have any over current protection not a big deal if you like living on the edge. Also it looks to me like it's a 3 pole to me. Not counting A1 and A2 I'm only seeing 6 screws/lugs 3 on top and 3 on bottom. If that's the case you need a 4 pole or you might be able to add a NO aux to the side of it. I'm not sure the size or the motor your running more than likely you need what's called a size zero motor starter and you need a 208/240 coil unless you got your heart set on low voltage that's gonna open a different can of warms. The guy above me drawing is good if it's a four poll contactor. It's not drawn how I would draw it his way would actually be easier to understand.
 

British Steel

Active User
Active Member
Joined
May 12, 2011
Messages
691
Likes
523
#11
Hi Mike,
If EvilBaying you want either a 4-pole or 3-pole-with-NO-aux (may be listed as "3NO+NO" or similar), and it must be rated for the motor - motors are the "AC3" rating in kw or hp marked on the contactor - this will be the LOWEST marked as motors/transformers are inductive and Hard Work, generating high voltages when the load current' S interrupted with bigger arcs at the contacts...
If you want to be extra safe, 24v control circuits can't fry you, you'll need a 24v a.c. coil contactor and a 208-24v control transformer rated about 50 va - and as suggested, a motor overload that sits between motor and the contactor, either fixed for your motor's full load amps or with an adjustment covering that current - the setting is such that it'll run at FLA but trip 20 - 30% above, saving the motor.
Check the motor voltage is right for your supply or it can be wired for it, and if it's never run in your sight check it for opens, leakage to earth etc!

Dave H. (the other one)
 

Reeltor

Active User
Active Member
Joined
Nov 18, 2014
Messages
737
Likes
308
#12
Guys, thanks for the input and ideas. I will need some time for this info to sink in.
Let me ponder and I'll be back with questions.

Thanks again
 

Reeltor

Active User
Active Member
Joined
Nov 18, 2014
Messages
737
Likes
308
#13
Well, it looks like the GE CL45 contactor will not work; I really think a low voltage on/off is best.
This older Craigslist contactor is rated for the correct amperage/motor and appears to me to have the motor overload but I don't see what the coil voltage is (I am assuming that it is line voltage 240v). Unless someone can decypher the GE serial number and it has what the coil voltage is, this one won't work either.
GE CR354AB3AB3AC CONTACTOR.JPG GE Contractor, AUX overload N.C..JPG GE coil, unknown voltage.JPG

While searching on eBay I didn't find what I was looking for but did find a advertisement and saw these Fuji contactors. The coils are available as 24vac or 24vdc. I assume that 24vac is what I should look for and maybe pull an old transformer off of a HVAC unit.

thanks for looking, on edit, here is the website where I saw the Fuji contactors https://www.automationdirect.com/ad...ols/Fuji_Contactors_-z-_Overloads/9_to_25_Amp

Mike
 

Attachments

British Steel

Active User
Active Member
Joined
May 12, 2011
Messages
691
Likes
523
#14
Hi Mike, please be aware that the overload in the pdf you attached is only up to one and a half amps, your motor may draw a lot more...

I tried to read the data on the motor plate in your earlier pic, but can't make out much other than the 60 cycles and 1740 RPM, if you can get a clear shot someone here may be able to offer a bit more guidance - it can help to wipe something dark over the plate with a rag so it fills in the stamped letters/numbers (I like artists' oil paint, or heavy graphite grease :D )

One and a half Amps would be around 3/4 - 1 HP at 440v, about half that at 220 - the motor plate LOOKS LIKE it has diagrams for high and low supply voltages, but it's hard to be sure with the fuzzy pic... It may give full-load amps as well, for the high and low voltage connections, if you're lucky!

Dave H. (the other one)
 

Reeltor

Active User
Active Member
Joined
Nov 18, 2014
Messages
737
Likes
308
#15
The motor is 220 or 440, I'll be using the low voltage-- 220v and it is tagged as 13.2 amps and 5hp.
I'll need to look at that website to see the correct overload.

I agree the photos posted are all fuzzy, they are sharp on my computer, I hate out of focus photos. It might be how I'm uploading them, I don't know
 

Reeltor

Active User
Active Member
Joined
Nov 18, 2014
Messages
737
Likes
308
#16
Update on the Shaper and motor. I wanted to be sure that the motor actually worked before I bought the contactors to wire up the switch so I wired the motor directly to the disconnect. Put the 3-phase to it and it ran smooth and quiet. The shaper was built for the Navy in 1943 and the motor looks original to me; even with the ugly porch paint. I'm planning on ordering the contactors in the morning.

This is the first oil lubed motor that I've seen. On each bell there is a thumb screw with a neat little hinge to keep the thumb screw with the motor.
Here are a couple of photos of the oiling ports

GREASE FITTING 2.JPG On the top there is a square plug that has a small screw. They were thinking when they designed the thumb screw; putting a split in the middle for a screwdriver and the hinge to prevent loosing it.
Left side of motor, from top.JPG
The opposite side is missing the screw,
Right side of motor from top Grease_Oil filling.JPG
 

GoceKU

Active Member
Active Member
Joined
Jul 14, 2017
Messages
253
Likes
399
#17
Mike, restoring older machines a person must learn new skills, one thing i've learned in the electrical many older machines use 24v magnet on the contactor, and run an transformer, mostly because the insolation wasn't very good and operator won't get electrocuted, when ever i come across any good contactor on flea market i'm checking for the little tug for the voltage on the magnet, and i'm keeping spare for all my machines, the 24v are hard to find even new here, the grease fittings on motor is not a bad thing, they last forever if sized right, i've been told you need to use thick oil like 90 weight.
 