Greetings
I am bringing a subpanel into my shop so I can install a 240V circuit for a VFD conversion on my RF31 clone mill. My main panel is right on the other side of the exterior wall from where I am planning to install the subpanel. My main is full, but I currently have a 50A GFI breaker for a hot tub. I intend to use that space in the main and install the GFI hot tub breaker in the subpanel - about 5 feet away (but probably 15 feet of wire as it needs to go up through the top plate of the wall across the top of a window, and back down). Ultimately I want to ditch the hot tub, but my wife likes it in theory even though it only gets used a few times a year. Here are some questions:
- An electrician friend of mine indicated that putting a 60A breaker in the main to feed the subpanel would work and #6 wire should be fine with that sort of a run. From what I can tell that checks out.
- I have a 2HP three phase motor that will run off the VFD and from what I understand that size motor will only draw about 6 amps. From looking at my local home improvement store, it seems that 20A is about as small a breaker that I can find for 240V circuits. Is that oversized?
- In my mind I had thought that this circuit would require huge conductors, but from what I can tell 12ga wire will handle this load easily. Does that sound right?
I think I have this worked out but I figured some of you have probably done this before so any tips or advice is appreciated.
Thanks
Tom
I am bringing a subpanel into my shop so I can install a 240V circuit for a VFD conversion on my RF31 clone mill. My main panel is right on the other side of the exterior wall from where I am planning to install the subpanel. My main is full, but I currently have a 50A GFI breaker for a hot tub. I intend to use that space in the main and install the GFI hot tub breaker in the subpanel - about 5 feet away (but probably 15 feet of wire as it needs to go up through the top plate of the wall across the top of a window, and back down). Ultimately I want to ditch the hot tub, but my wife likes it in theory even though it only gets used a few times a year. Here are some questions:
- An electrician friend of mine indicated that putting a 60A breaker in the main to feed the subpanel would work and #6 wire should be fine with that sort of a run. From what I can tell that checks out.
- I have a 2HP three phase motor that will run off the VFD and from what I understand that size motor will only draw about 6 amps. From looking at my local home improvement store, it seems that 20A is about as small a breaker that I can find for 240V circuits. Is that oversized?
- In my mind I had thought that this circuit would require huge conductors, but from what I can tell 12ga wire will handle this load easily. Does that sound right?
I think I have this worked out but I figured some of you have probably done this before so any tips or advice is appreciated.
Thanks