I have a need to do welding about 40 to 50 feet from my 220V power source. My welder is a Hobart Handler 190 mig. Max amps input at rated load is 20.5. I'm thinking 8 gauge would do it but am wondering if 10 gauge would work. I'm electrically literate limited but my understanding on welder extension cords is that voltage drop is not good for the machine or the quality of the weld. So what gauge wire do I need for an extension cord? What's your opinion on two 25' cords vs. one long one? I realize the wire gauge will be the same as one long cord.

Thanks,


Tom S.
 
Hey Tom, Any chance you can get a hold of the manual for your machine. The manual for my machine clearly lists the extension cord requirements. My machine is a Millermatic 210 and I can run a 100 feet on a 10 gauge (I think, it might be 8ga). Just a suggestion.
 
One long cord will always be better than two short ones. Every time you have a connection, you have the possibility (probability) of voltage drop across the resistance of the connection. #10 AWG cable with properly made up terminations should work for you. Larger wire will be even better, though not always necessary.
 
Tom,

You can use the 10# and like Hawkeye said, stay away from intermediate connections. If you're setting-up shop long term and will be doing a lot of welding at the higher Amperages, go with 8# in case you get a larger welder.

With 10#, you're losing 2 Volts. With 8#, only 1.2V loss.


http://www.calculator.net/voltage-d...ance=50&distanceunit=feet&amperes=20&x=69&y=8

Also, if you're buying a pre-made cord, make sure you get the right outer casing type if the cord will be left laying in the sun and exposed to the elements for days on end. Indoor rated cords will crack/deteriorate quickly. Here's a PDF that describes the cord markings such as S for hard use, W for UV and moisture resistances etc...

http://home.mchsi.com/~gweidner/extension-cords.pdf



Ray
 
Thanks everyone for your input. Now it's time to go shopping!
 
I have a need to do welding about 40 to 50 feet from my 220V power source. My welder is a Hobart Handler 190 mig. Max amps input at rated load is 20.5. I'm thinking 8 gauge would do it but am wondering if 10 gauge would work. I'm electrically literate limited but my understanding on welder extension cords is that voltage drop is not good for the machine or the quality of the weld. So what gauge wire do I need for an extension cord? What's your opinion on two 25' cords vs. one long one? I realize the wire gauge will be the same as one long cord.

Thanks,


Tom S.

when running wiring in the shop from the panel to the recepticale you take the rated load X 1.25. this gives you the amperage to go to the chart with. The charts are based on 100' runs with a max of 3% voltage drop. If you go over 100' you need to do the resistance calcs.
So 20.5 X 1.25= 25.6 o the charts #10 is sufficient for 30 amps #8 45 amps #6 60 amps.

My 230 amp welder draws 39 so 39 x 1.25=48.75 I ran a #6 and it runs fine with a #8 30' cord


hope this helps


Art
 
USED TO run 300 ft across casinos with 10 ga..still had plenty to weld 1/4 plate
 
I would prefer the 8ga so long as the price difference is too much but the 10 ga should do just fine. Keep in mind that it is a welder, so the load it is drawing is not continuous. Actually the higher the welding current the shorter the weld periods should be. Check the cycle duty of the welder for this information. During the time you are grinding and chipping will allow the cord to cool a little in between.

Keep in mind that my thoughts are on the cord and connections over heating not any voltage drop damage to the welder. Not that I think that there would be.
 
when running wiring in the shop from the panel to the recepticale you take the rated load X 1.25. this gives you the amperage to go to the chart with. The charts are based on 100' runs with a max of 3% voltage drop. If you go over 100' you need to do the resistance calcs.
So 20.5 X 1.25= 25.6 o the charts #10 is sufficient for 30 amps #8 45 amps #6 60 amps.

My 230 amp welder draws 39 so 39 x 1.25=48.75 I ran a #6 and it runs fine with a #8 30' cord


hope this helps


Art

Thanks Art. I ended up buying a 50' #10 extension cord and the appropriate receptacle and plug. Cut the ends off the extension cord and wired up the receptacle on one end and the plug on the other. Works great and it was significantly less expensive than buying a ready made welder extension cord.

Tom S.
 