I am trying to wire up a jog button to my VFD but the button is not working correctly and I wonder if I'm wiring it incorrectly.
I am using one of these normally-open momentary button.
One side of the button is wired to X4 on the terminal control block (as described on P39 of the manual).
The other side of the button is wired to COM on the terminal control block.
My problem:
When I press the jog button the motor starts (that's good).
When I release the jog button the motor continues running (not so good).
I also tried reproducing the problem with a jumper wire ... same problem.
When I jumper wire from COM directly to X4 the motor starts.
When I disconnect the jumper from X4 the motor continues running.
I configured the jog button function codes according to the manual as follows:
Thanks,
Chris!
As a side note ...
I did successfully wired up my VFD with start and stop buttons and a direction switch as described on P24 and P25 in the manual.
These buttons work great (after I realized I had o jumper the COM side of the start button to the X3 [input] side of the stop button)!
Below shows how I wired up the start and stop buttons and the direction switch.
And this shows how I set the function codes for the start and stop buttons and direction switch:
P0.02 = 1 (Terminal control)
03.01 = 1 (X1 used as Start terminal of 3-line control mode #1)
03.02 = 2 (X2 used as Direction terminal of 3-line control mode #1)
03.03 = 3 (X3 used as Stop terminal of 3-line control mode #1)
P3.07 = 2 (3 Line control mode #1)
I am using one of these normally-open momentary button.
One side of the button is wired to X4 on the terminal control block (as described on P39 of the manual).
The other side of the button is wired to COM on the terminal control block.
My problem:
When I press the jog button the motor starts (that's good).
When I release the jog button the motor continues running (not so good).
I also tried reproducing the problem with a jumper wire ... same problem.
When I jumper wire from COM directly to X4 the motor starts.
When I disconnect the jumper from X4 the motor continues running.
I configured the jog button function codes according to the manual as follows:
- P0.02 = 1 (Terminal control)
- P1.04 = 30 Hz (Jog running freq.)
- P1.05 = 4 (Jog acceleration time)
- P1.06 = 4 (Jog deceleration time)
- P1.21 = 0 (REV/JOG Key is set to JOG) (Jog works when I press the REV/JOG key on the FVD keypad)
- P3.04 = 4 (Use terminal X4 to control Forward Jog terminal)
- P3.05 = 3 (Use terminal X5 as Stop terminal of 3-line control mode #1)
- P3.07 = 2 (3 Line control mode #1) (Because I installed start, stop buttons and a direction switch which works great!)
Thanks,
Chris!
As a side note ...
I did successfully wired up my VFD with start and stop buttons and a direction switch as described on P24 and P25 in the manual.
These buttons work great (after I realized I had o jumper the COM side of the start button to the X3 [input] side of the stop button)!
Below shows how I wired up the start and stop buttons and the direction switch.
And this shows how I set the function codes for the start and stop buttons and direction switch:
P0.02 = 1 (Terminal control)
03.01 = 1 (X1 used as Start terminal of 3-line control mode #1)
03.02 = 2 (X2 used as Direction terminal of 3-line control mode #1)
03.03 = 3 (X3 used as Stop terminal of 3-line control mode #1)
P3.07 = 2 (3 Line control mode #1)