- May 11, 2017
- 232
I did some very basic wiring of my Hitachi VFD to my new lathe, shooting to successfully get through the "powerup test" described on page 2-23 of the hitachi manual.
wiring as such:
You can hear it here: https://bit.ly/3lsnYSC I pressed RUN, the motor accelerated towards 60hz, at about halfway I pressed stop and you can hear it decel.
Any thoughts from the experts?
I did notice something odd when I connected via the ProDriveNext software - it said my "region" is JPN, vs US
EDIT - I verified through reading all the parameter values using the PC program that the A082 and B012 values are right (my 6.6 was divided by 8.0 for a value of 82.5% in location B012, and the right code for 220v was in A082).
wiring as such:
- 240 volts to the VFD's L and N terminals, ground to the VFDs ground, verified it's 240 to the VFD.
- U V AND W OF the VFD to U V and W of the motor, and grounded
- At A082 (AVR voltage select), the book says the dsiplay should say A230 or A400 depending on 200 or 400 class, but mine showed actual voltages, and I scrolled through till I hit my motor nameplate voltage (220) and pressed set.
- At B012 (thermal overload setting) the book says I should see B160 on the display, but I see the inverter's current rating (8.0a) and the range of values is 0.0-8.0. Manual says I should make this my motor's current so I did (6.6)