- Joined
- Sep 1, 2023
- Messages
- 76
I have a 3 phase 2HP motor that draws 5.8Amps at 240v
I got HuanYang VFD to drive it, with the following specs:
(The motor will power a lathe, and while I could go into more details about the motor upgrade option, I would prefer if the thread stayed focused on the sizing question).
In the VFD manual (page 14), it is written: size the input breaker at 1.5x to 2x the rated current of the inverter.
Which translates into a breaker between [54 and 72], i.e. a 60Amp breaker.
From wire gauge tables I have found on the internet, the wire size for that breaker is from 4 to 6 AWG.
It's an awfully big wire.
First questions: did I get the breaker and wire sizing correctly ?
If so, is it possible to downsize the breaker (and wire), if I abandon the option of upgrading the motor ?
Downsizing the breaker is based on the assumption that I would only ever run the 2HP (5.8 Amps) motor on it.
The VFD 3-phase output at 18.5 Amp, is 1/3 the current draw of the motor (5.8 Amp).
Does this mean I can size the breaker at 1/3 of it's capacity (36 amps) between x1.5 and x2 ?
This would give me:
If I ever feel need to upgrade the motor, then I would change the wire and breaker, it turns out the lathe is only 5 feet from the panel.
I got HuanYang VFD to drive it, with the following specs:
- VFD rated power: 4kW
- 1-phase input: 36 Amps
- 3-phase output: 18.5 Amps
(The motor will power a lathe, and while I could go into more details about the motor upgrade option, I would prefer if the thread stayed focused on the sizing question).
In the VFD manual (page 14), it is written: size the input breaker at 1.5x to 2x the rated current of the inverter.
Which translates into a breaker between [54 and 72], i.e. a 60Amp breaker.
From wire gauge tables I have found on the internet, the wire size for that breaker is from 4 to 6 AWG.
It's an awfully big wire.
First questions: did I get the breaker and wire sizing correctly ?
If so, is it possible to downsize the breaker (and wire), if I abandon the option of upgrading the motor ?
Downsizing the breaker is based on the assumption that I would only ever run the 2HP (5.8 Amps) motor on it.
The VFD 3-phase output at 18.5 Amp, is 1/3 the current draw of the motor (5.8 Amp).
Does this mean I can size the breaker at 1/3 of it's capacity (36 amps) between x1.5 and x2 ?
This would give me:
- min = 36*(1/3) * 1.5 = 18
- max = 36*(1/3) * 2 = 24
If I ever feel need to upgrade the motor, then I would change the wire and breaker, it turns out the lathe is only 5 feet from the panel.