Doerr 3 phase motor- 440 or 220?

Reddmax

Registered
Registered
Joined
Jul 28, 2013
Messages
9
I have a 2557 Logan lathe that I purchased at an auction. It's in good condition, however I don't know if its wired for 220 3phase or 440 3phase. The motor faceplate says it can run on either, however I've never worked with a 60s era Doerr motor and I can't find specs on the web. Does anyone have an idea?

Redd
 
Hi Red,

if it's a dual voltage wye wound motor it's pretty easy to tell.

look at the tap configuration.

if wires (4,5,6) are bound together and (1,7) ( 2,8 ) and ( 3,9 ) are paired up and have main power fed to them,you have a motor that is wired for 220

if wires (4,7) (5,8) (6,9) are paired up and wires ( 1 ) ( 2 ) ( 3 ) all have main power wires fed to them you have a 440 wired motor.

i hope the info helps out

let me know if you need help, i can walk you through it

mike:))
 
Last edited:
Mike,

Your description was spot on. 4 through 6 are joined, plus the other three legs are as noted. Thank you so much for your input. I have ordered a 2 hp Hitachi VFD for phase conversion and control and will hopefully be powering up the beast this week.

Redd