A few months ago I converted my small milling machine from 120V single phase to 230v 3 phase using a China inverter. The project went great, and it is easily one of the best improvements I ever made to my shop!
Now I want to convert my JET 12-36BD lathe to three phase. But running a 230v line to that area of the shop will be a bear.
I see there are 110v single phase to 3 phase inverters available for up to three HP. I would be using a 2HP 3 Phase motor.
My confusion is the specs for these 110V inverters all say they output 110V AC.....Is this per leg? I don't believe there is such a thing as a 110V 3 phase motor?
Currently I have three 10g THHN wires in conduit going to the lathe. I also have other 120v devices on this same circuit so I can't simply use it for a 230v inverter. Or can I run 230V and use one leg for the 120V feeds?
Any suggestions and help is greatly appreciated.
Thanks in advance!
UPDATE: After some research I decided to use the exact same devices I used on my Milling machine conversion. I did not know that you could have two outlets on a single 230v circuit. I thought I had to run a totally separate 230v line for the lathe. Since the Milling Machine and Lathe are no more than 6' apart, I'm going to simply tap off that feed. There is a double 20a CB in the panel with 10g wire running about 25 feet. If I remember correctly, The 230v VFD with a 2HP motor draws 9A. The lathe and mill will never be on at the same time, but it seems I'll be OK if that ever happens.
Now I want to convert my JET 12-36BD lathe to three phase. But running a 230v line to that area of the shop will be a bear.
I see there are 110v single phase to 3 phase inverters available for up to three HP. I would be using a 2HP 3 Phase motor.
My confusion is the specs for these 110V inverters all say they output 110V AC.....Is this per leg? I don't believe there is such a thing as a 110V 3 phase motor?
Currently I have three 10g THHN wires in conduit going to the lathe. I also have other 120v devices on this same circuit so I can't simply use it for a 230v inverter. Or can I run 230V and use one leg for the 120V feeds?
Any suggestions and help is greatly appreciated.
Thanks in advance!
UPDATE: After some research I decided to use the exact same devices I used on my Milling machine conversion. I did not know that you could have two outlets on a single 230v circuit. I thought I had to run a totally separate 230v line for the lathe. Since the Milling Machine and Lathe are no more than 6' apart, I'm going to simply tap off that feed. There is a double 20a CB in the panel with 10g wire running about 25 feet. If I remember correctly, The 230v VFD with a 2HP motor draws 9A. The lathe and mill will never be on at the same time, but it seems I'll be OK if that ever happens.
Last edited: