I talked to Matt about this and he said to post my question on the PM thread, and since I do own a PM1440GT and a PM band saw I thought it was a OK fit.

I have a older Jet JTM-1 mill step pulley that has a 2HP, 2 speed, 3 phase motor. The motor plate has this info on it: Hz 60, Pole 2/4, 6.2/5.6 Amp, RPM 1720/3450, Class E. I have seen a lot of info regarding VFD installs, enclosures, switches etc. What would be the best fit for the mill? I don't need anything too fancy just functional. Thanks for your time!
 

tweinke

Active User
H-M Supporter-Premium Member
Joined
Mar 24, 2014
Messages
659
Likes
356
#3
Sound like a good plan to me. Seems funny that you've only gotten one reply so far. Could be a good idea to repost in the questions and answers section or the like.
 

darkzero

Global Moderator
Staff member
H-M Supporter-Premium Member
Joined
Nov 27, 2012
Messages
2,993
Likes
1,713
#4
This is not really related to PM since it's about a Jet machine. Regardless, machine brand doesn't matter here since you're looking for info on a VFD. Moving this to electrical, hopefully you'll get some more views over there.
 

Superburban

Active Member
Active Member
Joined
Jan 2, 2016
Messages
301
Likes
244
#5
I talked to Matt about this and he said to post my question on the PM thread, and since I do own a PM1440GT and a PM band saw I thought it was a OK fit.

I have a older Jet JTM-1 mill step pulley that has a 2HP, 2 speed, 3 phase motor. The motor plate has this info on it: Hz 60, Pole 2/4, 6.2/5.6 Amp, RPM 1720/3450, Class E. I have seen a lot of info regarding VFD installs, enclosures, switches etc. What would be the best fit for the mill? I don't need anything too fancy just functional. Thanks for your time!
Biggest issue I see, is the 2 speed motor. VFD's do not like any switches on their output side. I would look at either an interlock, so the VFD is turned off, before the motor speed control can be changed. Or lock the switch in one position, and use the VFD to control the speed.
 

f350ca

Active User
Active Member
Joined
Jul 11, 2013
Messages
1,181
Likes
1,843
#7
I was in touch with Automation Direct with regards to using the VFD listed above with a two speed motor. Their tech said no problem, just don't switch the two speed switch while the motor is running. No need to turn off the input power to the VFD. I've been using it on a radial arm drill press and it works fine.

Greg
 

Ulma Doctor

Infinitely Curious
Active Member
Joined
Feb 2, 2013
Messages
4,298
Likes
3,495
#8
sorry to be late to the party timberg,
Teco make a wonderful VFD in the Hp range you want- easy to set up and run- good manuals
Huanyang makes a decent quality, inexpensive VFD also- i have 3hp VFD on my Shenwai 1236 lathe-
it works great, easy to set up and program- the manual is written in funny Chinglish in a lot of places but understandable
Omron/Yaskawa make quality drives that are industrial quality, (kinda on the expensive side) a bit more involved to set up and program- great manuals
Lenze makes excellent VFD's too, price is expensive- programming/set up is more involved- great manuals
 

timberg

Iron
Registered Member
Joined
Dec 7, 2016
Messages
13
Likes
1
#9
Could I just remove the High/Low/Rev/Fwd switch and wire straight to the motor and use the VFD itself. Being a two speed I'm still not clear on how to hook that up. I'm also leaning towards the Hitachi drive with an additional cable to remote. Thoughts?
 

Ulma Doctor

Infinitely Curious
Active Member
Joined
Feb 2, 2013
Messages
4,298
Likes
3,495
#10
yes you can remove the switch and wire the motor direct.
you'll most likely use the low speed windings and overspeed the motor to 120hz, to gain full operational rpm of the motor.
you could go the other way, and use the high speed windings and operate the motor at 30Hz, if that proved to be more advantageous.
Hitachi also makes high quality VFD's, a remote panel is a great idea
 

Karl_T

Active User
Active Member
Joined
Oct 14, 2014
Messages
810
Likes
281
#11
2nd UD. Hitachi is a bit better VFD. I think you should wire it on the low windings for better low end torque
 

f350ca

Active User
Active Member
Joined
Jul 11, 2013
Messages
1,181
Likes
1,843
#12
I'd leave the HI/LO switch connected. Why limit yourself. Just don't switch it when the motor is running.

Greg
 

mksj

Active User
H-M Supporter-Premium Member
Joined
Jun 12, 2014
Messages
1,451
Likes
1,636
#13
I have tried to use a hi/low configuration on VFDs using two speed motors, but my tries to wire the VFD to operate/use both speeds has been lack luster and often with disappointing results. This includes programming the VFD for both motor settings, which many VFDs include in their setup. My experience is to wire the motor for the low speed motor setting and directly wire this to the VFD. The motor connections should be clearly marked on the motor/connection cover. There are some exceptions, I have not dealt with 2 speed constant Hp motors in VFD conversions. You can comfortable over 1750 RPM speed (4P) motor to 1.5X it base speed of 60 Hz. Two pole motors (3450 RPM) usually are limited to 1.25X their base speed, I usually do not over speed them. You could push a 1750 RPM motor to 2X its base speed, but unless it is an inverter motor, there are some performance drop offs. Since high speeds are usually associated with smaller end mills/drills, you probably will never notice the difference and this is what I would recommend. Since the motor was already designed for this speed, cooling and bearings should not be an issue. You also gain motor performance by over speeding because of the ratio of motor speed to spindle speed. Torque wise, a 2P motor spins twice as fast but had 1/2 the torque of a 4 pole. When you add it all up with gearing/drive ratio to get the same spindle speed, I think it is a wash on torque. Still, in my experience you get better motor performance using a higher number of motor poles using a VFD. Granted this is empiric observation from a number of installation.

VFD wise recommendations, well it all depends on your budget and application. I would say 80% of the VFD builds/installs I have done have used the Hitachi WJ200, and it works well and has been reliable. Kind of middle of the road. Teco VFDs comes in many flavors and models, I would recommend a Teco (or most any other VFD) over an HY for numerous reasons. The HY may be more "economical" for especially for larger "single phase" input applications in the 3+ to 10Hp, but reviews and from other forums and VFD gurus really question both the build quality and the stated claims. It is the only VFD that I have heard of routine failures, so hit or miss, at a price point. Cheap it is works, Automation Direct has commendable VFDs, and their manuals and Tech support is great, but their VFD models are becoming dated, so like their popular GS2 model does not run sensorless vector control (I would go with the GS3), which provides significantly better motor control at lower speeds, and the GS2 is somewhat limited in the programming department. Still, on a mill it is more run forward, stop, run backward commands and a speed pot. Many people over think VFDs and the myriad of programmable parameters, when it comes down to it, in most hobbyist application there are only a few parameters to set to get your machine running. Many/most of the parameters are for much more complex applications. Yaskawa makes very nice drives, along with ABB, and a few other higher tier manufactures. In this application, I can't say that you would see any difference. Since I tend to design a bit more complex VFD systems with "more features" I use drives with more programming flexibility and inputs.

There are a number of posts regarding installation of a VFD on mills, wire the VFD directly to the motor, wire the VFD input to power via a disconnect preferable using a breaker or quick acting fusing. Use a remote pod for a speed pot, E-Stop, and run controls. The run commands/controls can be 2 wire control using a Forward Off Reverse switch just closing the input contact, or 3 wire control with momentary Stop, Run and motor direction. With 3 wire control that uses momentary controls, in most case will not auto start if power is applied vs. 2 wire. Most VFDs also provide a setting so the VFD will not run if powered up in a run commend mode. This does work, I have tried it on several VFDs. So some basic skills, but a VFD on a mill works very well in most applications, usually stepped pulley drives are preferable to the mechanical varispeeds.
 

timberg

Iron
Registered Member
Joined
Dec 7, 2016
Messages
13
Likes
1
#14
I ended up ordering a Lenze AC Tech - ESV152N02YXB for this application along with a box with Start, Stop, FWD-REV switch and potentiometer. I know there are other and less expensive drives available and thought it was a good fit and all should be here in about a week. This will be wired from a separate 230, single phase rather than using the 3 phase RPC and if it works well, I'm might be ditching the RPC for entirely for VFD's. As far as the box with the Start, Stop, FWD-REV switch and potentiometer, what wire should I be using? A tech from the outfit that I purchased the drive from stated I should use a 9 or 10 conductor, 18 gauge, shielded wire, and I said OK. Started looking around on a few sites, not really finding what I was looking for unless I want to buy a whole roll, Not! I only need 8-10 feet. What are others doing. I'm probably getting wrapped around the axle on this one. lol Thanks in advance!
 

Ulma Doctor

Infinitely Curious
Active Member
Joined
Feb 2, 2013
Messages
4,298
Likes
3,495
#16
+1 on what Karl said.
i have scores of VFD's in the machinery i repair.
the manufacturers of the machinery do not use shielded wire for their installations
we do not work in areas that have interference, nor do our machines produce interference .
i think it is safe to run your equipment without shielded cables
 

mksj

Active User
H-M Supporter-Premium Member
Joined
Jun 12, 2014
Messages
1,451
Likes
1,636
#17
I think it is safe to use unshielded wire for short runs, like in a mill, as others have mentioned. But I have seen/had issues with VFD electrical noise interference. There are posts in other machinist forums dealing with VFD electrical noise causing false signaling, but this is usually with much longer runs between the VFD/Motor/Controls (and sometimes poor wiring). Do not connect the motor cable to the VFD signal wires or speed pot cable. Often VFD electrical noise can be picked up by radio and TV, and I have had to add RFI/EMI filters to the VFD input and also shield the VFD/motor cable to reduce the interference. You can also see increase electrical noise in the speed pot if remotely located, so if more than a couple of feet I prefer to use 3 or 4 wire 20G shielded cable, and I also adjust the VFD speed setting filter. This is low level, but you can see it as jitter in the speed Hz displayed. Many VFD equipped commercial machines have electrical input filters, and the VFD wiring is often internal to a grounded enclosure. Wires may be separated as to control voltages/mains voltage and wires may be twisted to decrease electrical noise.

Electrical grounding is a strange one, and not always what you expect. In general try to bring all your earth grounds to one point in the VFD cabinet or main power input (Star Ground). There are different options if you do use shielded wire as to grounding one end (usually at the VFD end), both ends, or neither (floating). There are also different cable/shield configurations which may also affect the grounding. In one install, the tach meter went wild when the cable shield was grounded in a VFD system. It only worked if the cable shield was floated at both ends. Anyway, should not be an issue with short wiring runs. As far purchasing cabling in short runs, as others mentioned eBay is a decent source, there are some online vendors that sell shorter runs but the shipping can bite you.
 

timberg

Iron
Registered Member
Joined
Dec 7, 2016
Messages
13
Likes
1
#18
All starting to come together, new breaker box installed, drive and controls arrived yesterday, and drive control wire/cable should be here by Friday. I picked up a Hoffman enclosure today. I'm stoked and pretty confused to be honest. A few things I could use your guidance with; a. connecting the motor, being a two speed I would like to use the low speed side as per previous recommendations, at the motor box, I have the six wires U1,V1,W1(black) and U2,V2,W2 (red), which ones do I use and what do I do with the other 3? I've read somewhere on the many forums they are tied together. b. Control box with individual buttons for Start, Stop, a switch for fwd/rev and a pot, would the start and stop buttons be considered a three wire between them both ( found that on Marshall Wolf, http://www.wolfautomation.com/media.../actech-smvect-nemafourx/actech-smvwiring.pdf. Any other guidance is greatly appreciated. motor box (2).JPG switch box.JPG
 

Bob La Londe

Active Member
Active Member
Joined
Apr 19, 2014
Messages
237
Likes
127
#19
I have Delta, Huan Yang, Hitachi, Mitsubishi, and one without a name on it. (Came on a machine). None have given me any troubles except when I overloaded them and tripped their internal overload protection. Press reset and I am good to go. I have heard a few (marginally few when you consider how many there are) more negative comments about Huan Yang than the others, but most problems seem to be spindles and setup which is not always easy for the neophyte.
 

Bob La Londe

Active Member
Active Member
Joined
Apr 19, 2014
Messages
237
Likes
127
#20
I have heard that there are some Chinese Huan Yang counterfeits out there to watch out for on Ebay. I always buy from a long term Ebay seller with a lot of feedback and less than 0.5% negative. Then I review recent negatives to see if its bad product or just slow boat from China syndrome. Anybody selling significantly cheaper I just assume is questionable.
 

Karl_T

Active User
Active Member
Joined
Oct 14, 2014
Messages
810
Likes
281
#21
I'm going to differ to somebody else on your motor wires. I *think* just wire the VFD outs to one set or the other. It won't hurt to try. I'll guess one set is "lo" and the other is "hi"

There are several ways to wire your control. lets decide exactly what you want. My favorite method is to have a start and Estop for the whole machine. Push the big red stop button and kill everything. If you have nothing else like power feed, coolant, etc. you may not feel this is necessary. I spent too many years as a corporate slave where this is required on all machines. Any fool knew how to turn off any machine as they all had this.

For the VFD driving the spindle, I like a three position rotary switch, left is CCW, center is off, right is CW. really handy if you want to do things like power tapping. A plus, this is easy to wire with no additional relays needed.

Or we could have a start CW, a start CCW, and a stop button.

Or we could have a rotary switch for CW or CCW, a start and a stop button.

All of the above use a pot for speed control

I'll be glad to walk you through any of these options. Do you read ladder logic?
 

tweinke

Active User
H-M Supporter-Premium Member
Joined
Mar 24, 2014
Messages
659
Likes
356
#22
I'll be glad to walk you through any of these options. Do you read ladder logic?
No but if you hum a few bars I might be able too................... :cower:

In reality all this VFD stuff is interesting to me and I enjoy reading these threads.
 

timberg

Iron
Registered Member
Joined
Dec 7, 2016
Messages
13
Likes
1
#23
Thanks Karl; I did find a label on the back of the elec motor cover (imagine that), might be what I'm looking for. Mark mentioned using the 4P side for the 1720, or low side. Still confused about that. Ladder logic? Googled it, I don't think so, but I'm open to most anything new to learn.
. IMG_0737.JPG
 

Karl_T

Active User
Active Member
Joined
Oct 14, 2014
Messages
810
Likes
281
#24
I assume 2p means 2 pole and 4P means 4 pole. If so, the 4P connection is low speed. If i understand this correctly, hook your R S T terminals from the VFD to U1 V1 and W1. Do NOT bond U1 V1 and W1 together.

I actualy read your reference. It says how to do it Capture.JPG
 

mksj

Active User
H-M Supporter-Premium Member
Joined
Jun 12, 2014
Messages
1,451
Likes
1,636
#26
So the motor would be run on 4P with connections to U1, V1 and W1 and no connection to U2, V2 and w2. This is based on the cover diagram, the manual is attached. The maximum frequency could be either 100 or 120Hz if you need maximum speed. Please specify which VFD you are or plan to use and I can guide you to 3 wire logic connections. I have attached some picture diagrams as to some suggestions. Basic 3 wire should work, the WJ200 has some added features so there are some other inputs that can be used.

OK, just saw you ordered the ESV152N02YXB so the diagram above is for 2 wire, let me look at the manual for 3 wire control.

JTM-1 2 Speed motor wiring.jpg

On this VFD, the logic control is a bit different. All three are momentary buttons in the first, the second should also work which uses a maintained switch for reverse. This is not in the manual, but pased on the manual programming parameters.

3 wire Lenze.jpg
 

Attachments

Last edited:

timberg

Iron
Registered Member
Joined
Dec 7, 2016
Messages
13
Likes
1
#27
I must have did something right, powered up and did some basic parameters. I'm still waiting on some control cable for the remote before I do anything on the terminal strip. P108, Motor Overload, since I have a two speed motor and running it on the low side, which amp rating should I use? 5.6 or 6.2 for my %, I currently set it for 80% (low side) and I think the 6.2 came out to 87% or there abouts. I did have a little motor noise and changed the Carrier Frequency, P166 from 4kHz to 6kHz and seem to help. No chips yet, will wait till install is complete. Before I forget, Thank You all for your assistance!! these VFD's are pretty cool
 

Karl_T

Active User
Active Member
Joined
Oct 14, 2014
Messages
810
Likes
281
#28
You have more torque in Lo, that's why it is suggested. You are good for the higher amps - 6.2
 

timberg

Iron
Registered Member
Joined
Dec 7, 2016
Messages
13
Likes
1
#29
Not sure what I did wrong, but now I'm confused. The remote box that I'm using has (Start Button-normally open, Stop Button- normally closed, 2 position Forward/Reverse switch- normally open, and a POT) and there is a picture of it in a previous post. This is what it is doing; Press start with switch in FWD- good, Press Stop - good, Switch to REV - starts in REV without pressing start and while running I switch to FWD - continues running in REV, also while running in REV, stop button does nothing but pressing the start button it Stops? The tech at MWA told me to use this to wire it up http://www.wolfautomation.com/media.../actech-smvect-nemafourx/actech-smvwiring.pdf but I went wrong somewhere.
 

Karl_T

Active User
Active Member
Joined
Oct 14, 2014
Messages
810
Likes
281
#30
first off, exactly which page did you wire it to? The closest I see is two wire forward/reverse with speed pot. If you are using this one you'll need a latching relay on your stop/start buttons. As this VFD has many wiring options, lets be sure we are on the same page before going farther. I am looking at this one Capture.JPG


MKSJ posted another option, look back a few posts. this one needs no latching relay. If you are wiring that method, there will be programming parameter changes to the VFD.
 