Vfd Drive Question

Discussion in '++ ELECTRICAL POWER KNOWLEDGE BASE ++' started by jamesarnold26, Jan 6, 2017.

  1. jamesarnold26

    jamesarnold26 United States Swarf Registered Member

    Likes Received:
    1
    Trophy Points:
    3
    City:
    Sanford
    State:
    North Carolina

    -Return to Top-

    I'm just a hobby Machinist. I have three lathes, a BP J-head mill all with 3ph motors.
    This is what I'm thinking of doing.
    Getting a 5hp vfd drive and putting a disconnect box under it. Run the wires from the vfd in the top. Then run conduit from each machine to the bottom contacting all of them to the terminals. Use the machines on/off switches.
    It's only me working in the shop. So I can't see running two at a time.
    The largest motor is 3hp with the longest 3ph wire length being 20 feet to the BP 1hp.
    This would keep me from buying one vfd per machine.
    Would this setup work ?
     
  2. stupoty

    stupoty Active User Active Member

    Likes Received:
    208
    Trophy Points:
    63
    City:
    London

    -Return to Top-

    I belive most vfd's dont like running without a motor connected and may detect it as a fault condition and switch off.

    You could have a vfd with a three phase socket wired on the output and plug the diferent machines in, the motors would have to be simmilar in spec (poles, rpm, desired start stop speed) to play nice without changeing vfd settings.

    Stuart
     
    BillyT likes this.
  3. Eddyde

    Eddyde Active User H-M Supporter-Premium

    Likes Received:
    437
    Trophy Points:
    63
    City:
    Brooklyn
    State:
    New York

    -Return to Top-

    No, at least not easily. You cannot have any switches between the VFD and the motor. All control, direction, speed etc., must be done by the VFD so the machines control wiring must also go to the VFD, that would be difficult to do with multiple machines. The only way I could see such a scenario, would be to have the VFD connected to a receptacle and have a plug for each machine, so that only one machine could be connected at a time. Control would be via a pendant on a long cable that you would have to bring to the machine you want to use. Not very convenient IMHO.
     
    mksj likes this.
  4. jamesarnold26

    jamesarnold26 United States Swarf Registered Member

    Likes Received:
    1
    Trophy Points:
    3
    City:
    Sanford
    State:
    North Carolina

    -Return to Top-

    Well aren't y'all just full of good news. Lol
    I was afraid that would be the answer. Thank you for the information and keeping me from wasting the money setting it up for nothing.

    Sent from my SM-G930V using Tapatalk
     
    markba633csi likes this.
  5. mksj

    mksj Active User H-M Supporter-Premium

    Likes Received:
    1,435
    Trophy Points:
    113
    City:
    Tucson
    State:
    Arizona

    -Return to Top-

    You would be better off with a single RPC (and probably less overall cost). These does not stop you from running a RPC and then using a 3 phase VFD on a particular machines if you need the speed control. A smaller VFD on a single machine would be more cost effective, but it needs to be wired into the controls. Three phase VFDs run fine off of RPCs in most cases. The limiting factor between a single phase and three phase VFDs is the ripple generated in the DC conversion process, single phase generates more ripple and needs higher rated diodes and capacitors. The ripple can also be minimized by the use of input or bus chokes which store and release energy (smooth the ripple). So an RPC uses the motor coils to produce a similar affect to generate the third leg.
     
    firestopper likes this.
  6. jamesarnold26

    jamesarnold26 United States Swarf Registered Member

    Likes Received:
    1
    Trophy Points:
    3
    City:
    Sanford
    State:
    North Carolina

    -Return to Top-

    be17634e2f88fd4e1af947886b507eee.jpg 61adbb61964e9e19782268e7939c4e00.jpg
    With a 20hp 3ph motor. I just don't know what else I need or how to wire it up.
     