Tig Welder

Discussion in 'ELECTRICAL ISSUES - POWER YOUR MACHINES & SHOP' started by sk1nner, Nov 22, 2015.

  1. sk1nner

    sk1nner United States Active User Active Member

    Likes Received:
    14
    Trophy Points:
    18
    City:
    Warren
    State:
    Michigan

    -Return to Top-

    I was given a Miller Econotig from work. It's said to work good. The only problem is that it runs on 460v single phase, 33 amps of it. I (obviously) don't have 460 in my garage. I removed the cover and inside was this diagram 20151106_190520-1.jpg I'm no electrition so I need some help figuring if I can convert it to 220 single phase. If this makes sense to anyone please, any info you can lend me is greatly appreciated. As always, thank you in advance.
     
  2. Hawkeye

    Hawkeye Canada Active User H-M Supporter-Premium

    Likes Received:
    375
    Trophy Points:
    83
    City:
    Kelowna
    State:
    British Columbia

    -Return to Top-

    The drawings themselves don't give an easy solution, but if you open the welder up and look at the main transformer itself, you might find extra wires or terminals coming out of it. If so, it's just a case of moving the second incoming wire to the appropriate terminal. You will be drawing quite a bit more current at 220V, so I'd plan on running a 50 amp welder outlet.

    An easy alternative would be to source a 220 - 460 transformer, but it would need to be around 20 KVA to give you full use of the welder. And again, that would need to be fed by at least 50 amps.

    If you do find extra taps on the transformer, post a picture so we can better advise you.
     
  3. sk1nner

    sk1nner United States Active User Active Member

    Likes Received:
    14
    Trophy Points:
    18
    City:
    Warren
    State:
    Michigan

    -Return to Top-

    I disn't see any extra wires inside, bUT i can taka a nother look. What I wonder is in the diagram I see there is a circle with FM inside if it. What does that mean? I calculated it out and I would need a 15180VA. Do you think a 15KVA transformer would be adequate? I've looked on ebay and I see a whole lot of 460 to 220 step down transformers, those can be used backwards to increase the voltage right? Thanks for the info
     
  4. TOOLMASTER

    TOOLMASTER you don't want to know Active Member

    Likes Received:
    1,046
    Trophy Points:
    113
    City:
    SOMEWHERE
    State:
    Minnesota

    -Return to Top-

    is there a sticker on outside with voltage in options
     
  5. sk1nner

    sk1nner United States Active User Active Member

    Likes Received:
    14
    Trophy Points:
    18
    City:
    Warren
    State:
    Michigan

    -Return to Top-

    Unfortunately no. It says 460 single phase 33 amps
     
  6. TOOLMASTER

    TOOLMASTER you don't want to know Active Member

    Likes Received:
    1,046
    Trophy Points:
    113
    City:
    SOMEWHERE
    State:
    Minnesota

    -Return to Top-

  7. David VanNorman

    David VanNorman United States H-M Supporter - Premium Content H-M Supporter-Premium

    Likes Received:
    130
    Trophy Points:
    43
    City:
    Wind Ridge
    State:
    Pennsylvania

    -Return to Top-

    If you was able to set it for 220 it would take like 66 amps to run it. I think you might put it on E-bay. It is not for a ham and egger.
     
  8. Hawkeye

    Hawkeye Canada Active User H-M Supporter-Premium

    Likes Received:
    375
    Trophy Points:
    83
    City:
    Kelowna
    State:
    British Columbia

    -Return to Top-

    You would need 15180 watts if it was a resistive load, but, since it is a highly inductive load, the VA should be rated higher.
     
  9. BarnyardEngineering

    BarnyardEngineering United States Active Member Active Member

    Likes Received:
    9
    Trophy Points:
    8
    City:
    Rochester
    State:
    New York

    -Return to Top-

    That's why it was free. If it were easily converted to 220V single phase, you never would've had a shot at it unless you're the only one that works at the shop.
     
  10. John Hasler

    John Hasler United States Active User H-M Supporter-Premium

    Likes Received:
    764
    Trophy Points:
    113
    City:
    Elmwood
    State:
    Wisconsin

    -Return to Top-

    FM most likely means fan motor. If I had it I'd seriously consider rewinding the primary for 240.
     
    brino likes this.
  11. Tony Wells

    Tony Wells United States Vice President Staff Member Administrator

    Likes Received:
    19,350
    Trophy Points:
    113
    Location:
    Tyler, Texas
    City:
    Tyler
    State:
    Texas

    -Return to Top-

    On the main diagram, T1 shows to have a 230 primary. The additional diagram is a supplement where it came factory wired for 460. Probably a different transformer. Before getting too excited about it, I'd get a price on a replacement T1. Yes, probably plenty of money, but cheaper than a whole new welder. Check that PC1 has the same inputs as shown. I would presume so, since there is no other schematic.
     
    whitmore likes this.
  12. sk1nner

    sk1nner United States Active User Active Member

    Likes Received:
    14
    Trophy Points:
    18
    City:
    Warren
    State:
    Michigan

    -Return to Top-

    Could you please elaborate on this? I've done a little bit of research but it sounded like I would need a thicker wire (they say it's magnetic?) And half as many windings. Does that basically cover it?
     
  13. sk1nner

    sk1nner United States Active User Active Member

    Likes Received:
    14
    Trophy Points:
    18
    City:
    Warren
    State:
    Michigan

    -Return to Top-

    From what I've seen it looks to be about $700 . Would a step down transformer used in reverse work? They seem to be a lot more affordable. Thank you
     
  14. John Hasler

    John Hasler United States Active User H-M Supporter-Premium

    Likes Received:
    764
    Trophy Points:
    113
    City:
    Elmwood
    State:
    Wisconsin

    -Return to Top-

    A step-down transformer in reverse would work. Be careful working with 480. It is more than twice as dangerous as 240.
     
  15. jim18655

    jim18655 United States Active User H-M Supporter-Premium

    Likes Received:
    303
    Trophy Points:
    63
    City:
    Shickshinny
    State:
    Pennsylvania

    -Return to Top-

    Connect as an autotransformer and you only need to carry half the current.
     
    John Hasler likes this.
  16. John Hasler

    John Hasler United States Active User H-M Supporter-Premium

    Likes Received:
    764
    Trophy Points:
    113
    City:
    Elmwood
    State:
    Wisconsin

    -Return to Top-

    I'd make the existing winding into two paralleled windings. Exactly how I did it would depend on what I saw when took it apart.
     
  17. Tony Wells

    Tony Wells United States Vice President Staff Member Administrator

    Likes Received:
    19,350
    Trophy Points:
    113
    Location:
    Tyler, Texas
    City:
    Tyler
    State:
    Texas

    -Return to Top-

    Using a stepup transformer is one way to go, but like John says, extra care around 480. It's not forgiving. I'm not really sure how that transformer would be to be sized, with out thinking about it some. You know the demand of the machine, but the transformers I have seen are rated for stepdown use. I suppose energy is energy and the same ratings would apply either way.
     
  18. sk1nner

    sk1nner United States Active User Active Member

    Likes Received:
    14
    Trophy Points:
    18
    City:
    Warren
    State:
    Michigan

    -Return to Top-

    So I could actually use the same wire, just double it up. That sounds interesting. I may look into this more. Thank you.
     
  19. jim18655

    jim18655 United States Active User H-M Supporter-Premium

    Likes Received:
    303
    Trophy Points:
    63
    City:
    Shickshinny
    State:
    Pennsylvania

    -Return to Top-

    Transformers aren't as efficient in "reverse" as they are in the way they're designed to be used. It has to do with the magnetic flux around the core and the position of the coils.
     
  20. Tony Wells

    Tony Wells United States Vice President Staff Member Administrator

    Likes Received:
    19,350
    Trophy Points:
    113
    Location:
    Tyler, Texas
    City:
    Tyler
    State:
    Texas

    -Return to Top-

    Makes sense.
     
  21. John Hasler

    John Hasler United States Active User H-M Supporter-Premium

    Likes Received:
    764
    Trophy Points:
    113
    City:
    Elmwood
    State:
    Wisconsin

    -Return to Top-

    Well, I said *I'd* consider trying it, but I'm an electrical engineer and also a little bit crazy. Whether or not I actually would try rewinding it would depend on what I found when I took it apart.
     
    sk1nner likes this.
  22. John Hasler

    John Hasler United States Active User H-M Supporter-Premium

    Likes Received:
    764
    Trophy Points:
    113
    City:
    Elmwood
    State:
    Wisconsin

    -Return to Top-

    They work exactly as well one way as the other.
     
  23. sk1nner

    sk1nner United States Active User Active Member

    Likes Received:
    14
    Trophy Points:
    18
    City:
    Warren
    State:
    Michigan

    -Return to Top-

    You have sparked my interest in doing this. I don't want to mess anything up, could you give some tips. I know I will have to be careful with the wire. But what else should I look for?
     
  24. sk1nner

    sk1nner United States Active User Active Member

    Likes Received:
    14
    Trophy Points:
    18
    City:
    Warren
    State:
    Michigan

    -Return to Top-

    Got a few pics of the inside of the welder. The main transformer actually has 3 windings on it
    20151123_215716.jpg 20151123_215647.jpg
    20151123_215634.jpg
     
  25. MozamPete

    MozamPete South Africa Active User H-M Supporter-Premium

    Likes Received:
    692
    Trophy Points:
    93
    City:
    Ladysmith
    State:
    Outside US / Canada

    -Return to Top-

    Looking at the first post with the circuit diagrams, I would say the fan motor is 230Vac in both configuration (230V or 460V supply), so if you just disconnected wire '11' from the switch to the transformer and reconnect from the switch to the transformer terminal wire '13' connects to you would get all the correct voltages out of the transformer when running on 230Vac (the 24V control supply, supply to the electrode, etc). You would probably still only be able to draw the original 33 amp from the supply without risking burning out the transformer primary so would need to de-rate the welder output to around 1/2 current - but you could easily add a fuse or circuit breaker to the input to protect against that and give it a try.

    Clipboard-1.jpg
     
    Last edited: Nov 24, 2015
  26. sk1nner

    sk1nner United States Active User Active Member

    Likes Received:
    14
    Trophy Points:
    18
    City:
    Warren
    State:
    Michigan

    -Return to Top-

    With wire 13 being 230v, logically wouldn't there be the other end of that wire somewhere? Or would it actually splice off of the 460 coil winding?
     
  27. MozamPete

    MozamPete South Africa Active User H-M Supporter-Premium

    Likes Received:
    692
    Trophy Points:
    93
    City:
    Ladysmith
    State:
    Outside US / Canada

    -Return to Top-

    That's what the circuit diagram is showing, 460v across the entire primary with a tap off half way for the fan motor (which I'm assuming is 230vac). It is called an auto transformer and can be done with only one winding needed, and also work the other way round - when you put 230v on as show in my markup you will get 460v at the unused end so make sure you insulate it and don't just leave a wire floating around.

    As you haven't increased the wire size you as still limited to the original transformer current limit - which is probably something just above the 33A quoted supply requirement, but how much above is unknown unless you can find some actual markings on the transformer.
     
  28. RJSakowski

    RJSakowski H-M Supporter - Premium Content H-M Supporter-Premium

    Likes Received:
    2,294
    Trophy Points:
    113
    City:
    Barneveld
    State:
    Wisconsin

    -Return to Top-

    According to the manual, there is over temperature protection circuitry so you could probably still use to full capacity, just derate the duty cycle chart accordingly.

    If the tap for the fan comes out from the winding (and is 230v), you may be able to split the primary winding there and reconnect the two halves as two parallel windings.
     
    MozamPete likes this.
  29. sk1nner

    sk1nner United States Active User Active Member

    Likes Received:
    14
    Trophy Points:
    18
    City:
    Warren
    State:
    Michigan

    -Return to Top-

    Thank you everyone for the help with this. You all are a great bunch of guys!
     
  30. sk1nner

    sk1nner United States Active User Active Member

    Likes Received:
    14
    Trophy Points:
    18
    City:
    Warren
    State:
    Michigan

    -Return to Top-

    Yes the fan is 220v. So I can input 220 to the "fan" lead (#13) and power the welder, this is great news. I really can't express how grateful I am for the info guys, you saved me a lot of time and money on this. Thank you!
     