Ebay Vfd

PD001: 0
PD002: 0
PD003:60.0
PD004:60.00
PD005:70
PD006:60
PD007:.50
PD008:220
PD0009:220
PD010:220
PD011:0
PD014:3
PD015:3

Everything else set to the default.
 
Try setting your carrier frequency to a different value. PDo41 I think
 
Try setting your carrier frequency to a different value. PDo41 I think
Ok. I will mess with it try 0 than go up by 5 and see if it gets better. Also once I hit run the motor turns on but the stop/rev buttons have no effect.
 
Regarding the Stop, make sure PD024 is set to 1

For a compressor, I would set stopping mode to coasting, PD026 = 1

For reverse, make sure that PD023 is set to 1, enable reverse
 
Regarding the Stop, make sure PD024 is set to 1

For a compressor, I would set stopping mode to coasting, PD026 = 1

For reverse, make sure that PD023 is set to 1, enable reverse
Those are set to that. Still no dice everything else seems to work as expected but once I hit run the only way to stop it is to hit the breaker. Also another odd thing. I can increase the speed by hitting up arrow however it wont decrease the speed that way. I can hit down arrow all I want and the display shows the freq value going down but the motor remains at the same speed even if I hit run. However setting perimeter 41 to 13 did make the motor run quieter. I emailed the vendor and asked his advice I'll let him know abouth the issue im having with it not stopping.
 
That is strange, those settings should work. You might try a system reset, PD013 =08, and start over on the parameters.
 
I bought the same brand and after a week of fooling with it I returned it and DID get My money back. The parameter for frequency adjust did nothing, at least Your motor runs, Mine did not even run the motor. Went with a rotary phase converter, no programing, started right up, just extremely loud. Muffs extremely needed.
 
A couple of comments on your parameters.
You should set the VFD to the motor specific parameters, PD141-144
Other suggests changes:
PD000 = 0
PD001 = 0
PD002 = 0
PD003 = 60.0
PD004 = 60.0
PD005 = 60.0 or 70.0
PD006 = 3.0
PD007 = 2.0
PD008 = 240
PD009 = *
PD010 = 15.0
PD011 = 4.00
PD023 = 1 (reverse rotation enabled if needed)
PD024 = 1
PD026 = 1
PD041 = 12
PD141 = 230
PD142 = 13.2
PD143 = 1725
PD144 = 4

When changing the frequency or stopping, you may need to enter the change for it to take effect, also the voltage and frequency parameter must support these changes, not sure why you would want a variable speed or reverse on a compressor. If it is still not responding to commands you could program/change the multi-inputs and try something like a 3 wire control with external switches. If you are not using the multi-inputs might try setting PD044-PD049 to 0. Do not have access to my notes on the VFD, so there may be a few other parameters that could be tweaked.

Not a big fan of this brand of VFD because of poor documentation and issues like these, but there is nothing close in this price range. I have been able to get them to work correctly, but I have heard that those sold on eBay may be missing their braking module, and have other support/warranty issues, which include the seller disappearing.