Tried several acceleration settings from 5-60 seconds, all with same result. Also bypassed drum switch. When I turn it on, the motor starts to move but almost imperceptibly, vfd clicks and error shows on screen.It also might be called something like trip current. But it doesn't sound like a settable parameter on your VFD.
The faster the motor spins up to speed the more current it will draw. By putting in a long spin up time you should be minimizing the current being drawn during spinup.
Is the VFD wired directly to the 3ph motor with nothing between them? No wires shorted? No funny grounding in the connections? If so it sounds like you have a bad VFD. I would expect your motor to at least budge before throwing the over current fault you describe if the VFD is working.
EDIT: You could put a clip on ammeter over one of the 3 phase legs between the VFD and the motor to see if ANY current registers... if you happen to have one. I would not worry too much about doing this though as it is probably your VFD.
Chuck